Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION 7650 IO registers

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7650 IO registers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
573
Mehran_Mehrnia
Mehran_Mehrnia Champion
210
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
ashley_accqrit_
ashley_accqrit_
Contributor

Posted: ‎2016-08-28 11:54 PM

0 Likes
4
1834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-28 11:54 PM

ION 7650 IO registers

Hello Everyone,

I am looking for the Modbus register list for the DIGITAL IO for the ION 7650 meter.

All the register l find have the electrical parameters but none have the Digital IO registers.

Please point me in the right direction.

Thanks team,

Ashley

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Anonymous user
Not applicable

Posted: ‎2016-08-29 02:05 PM

0 Likes
2
1741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-29 02:05 PM

Hi Ashley,

By default, the Digital IO is not included in the ION7650 meter's available modbus register list. However, you could get the digital IO information through modbus protocal by adding them into the meter's modbus slave module.

More information you could refer to the documents below:

http://www.powerlogic.com/literature/Modbus%20and%20ION%20Technology.pdf

http://www.powerlogic.com/literature/ION_Reference_70002-0290-03.pdf

Thanks

Leo

Reply
ashley_accqrit_
ashley_accqrit_
Contributor

Posted: ‎2016-08-29 11:42 PM

0 Likes
1
1741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-29 11:42 PM

Hello Chen,

Thank you for your reply,

My application is so simple and now becoming complicated due to the ION meter not have the IO associated to a register.

All i need is the status of the first 3 DI's. DI1 - 3 are going to be used as breaker indication, open, closed tripped on a SCADA.

Which module would i use to move the Digital inputs into a register to monitor the bits?

All the PM meters have a register to monitor the IO.

I look forward to your assistance.

Once again Thanks

Ashley

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2016-08-30 10:06 AM

0 Likes
0
1741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-30 10:06 AM

The documentation reference above will explain how to map the device's IO to a modbus register.  This will be a small framework you will need to paste to the devices you wish to monitor the IO on.  Think of it as configuring the IO port to be input, output, etc and then mapping that configuration to one or more modbus registers.

Remember that even the older PowerLogic devices had issues around the IO - interpreting the modbus register values is dependent on how the IO port is configured and that configuration still needed to be done to get the right values.

Reply
Anonymous user
Not applicable

Posted: ‎2017-11-28 11:58 PM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-11-28 11:58 PM

Useful Link:

How to access 7600 Input/Output through Modbus?

ION Setup 3.0 - Documents and Downloads | Schneider Electric

Create Modbus point for DI:

Hold down CTRL and click on the device in the left hand window

Capture 01.PNG

Capture 02.PNG

Capture 03.PNG

Capture 04.PNG

Capture 05.PNG

Capture 06.PNG

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore