Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION 7330/7350 limited number of connections over TCP

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: ION 7330/7350 limited number of connections over TCP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
570
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
engenharia_memt
engenharia_memt
Explorer

Posted: ‎2020-07-09 03:57 PM . Last Modified: ‎2024-01-30 05:21 AM

0 Likes
11
6341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 03:57 PM

ION 7330/7350 limited number of connections over TCP

Dear all,

 

I hope this message finds you well. 

navigating on some topics in the community, trying to find some way to connect two ION clients simultaneously to an ION 7330/7350 meter on TCP port (7700), I came accross a topic in which  @Hal_Etheridge al_Etheridge mentions that maybe there is a firmware version that could have this number of TCP connections extended to the maximum of two clients using ION protocol by disabling the serial port.

Could you guys confirm if this would still be a possibility and give me some more details on this subject? 

I appreciate any other ideas. 
Thanks in advance!  

 

Best Regards,

Ramon

Labels
  • Labels:
  • ION7000
Tags (3)
  • Tags:
  • ION 73X0
  • ion protocol
  • sockets
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-29 06:55 AM

1 Like
0
6287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-29 06:55 AM

Hello @engenharia_memt ,

 

Yes from the serial number I can determine if the meter came with a modem as well as Ethernet. The front optical port does not "kill" other ports. This is a separate port and the meter does not limit the number of serial ports.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 11
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2020-07-09 04:49 PM

0 Likes
0
6337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 04:49 PM

Long as it is the latest firmware version for the ETH73xx card and the meter itself then the feature should be there.  The Protocol register for one (or more) of the serial ports should have a "None" option.  Once that is selected then that "slot" is freed for an additional TCP connection.  I am not sure what version number it is.  Performance may be slightly impacted as internally the requests from the ethernet card is transferred to the main meter over a 19200 or 38400 baud serial link.  Typically this should not be noticeable but if you are hammering all the TCP connections at the same you may have some slowdowns.

 

Note that this is from a very long time ago so my memory may be slightly off...  I think the last firmware release for that product was around 15-20 years ago....

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-14 08:42 AM

1 Like
9
6327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-14 08:42 AM

Hello @engenharia_memt 

 

Please refer to https://www.se.com/ca/en/faqs/FA212335/, the ION73xx meter has a maximum connection of 1 for the ION protocol. The serial port does not have the none option. There is nothing that can be done to the number to support more than 1 connection with the ION protocol.

 

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-14 01:15 PM

1 Like
8
6325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-14 01:15 PM

Hello @engenharia_memt 

 

Looking at the KB again and talking with hardware team, you might be able to get a "second" ION connection. This does require that the com ports on the meter are tried together, Com1->Com2. One port is set to Ethergate (default) the second port is set to ION. Then you can use the device ID of the second com port and TCP port of the first com port to to the meter. I currently do not have an ION73xx meter I can confirm this with.

 

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
engenharia_memt
engenharia_memt
Explorer

Posted: ‎2020-07-14 01:40 PM

2 Likes
7
6323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-14 01:40 PM

Dear @Charles_Murison, 

 

thank you for helping in this case!

I think I got the required steps. We still have one or two pieces of ION 73xx in the lab, so we can perform some tests.

As soon as our team finish the tests, we update you here. 

 

Best regards,

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-22 04:22 PM

0 Likes
6
6306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-22 04:22 PM

Hello @engenharia_memt ,

 

Where you able to get the Ethergate to work for you?

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
engenharia_memt
engenharia_memt
Explorer

Posted: ‎2020-07-22 07:57 PM

0 Likes
5
6304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-22 07:57 PM

Hi @Charles_Murison, 

 

actually, no. I have an ION7350, which I jumped the serial com ports and left PME connected via ethernet 7700 port and configured a new connection from ION Setup using ethergate protocol on 7702 port. I don't know if I'm missing any step, but you can see most of configuration in attached picture. Also, you can see that Ethergate protocol is being used and I promise you that ION Setup simply timed out. Also, I tried to change ID on COM1 to 255, but nothing has happened.    

I appreciate if you could give any insight. 

 

Thank you!!

 

ION7350-config screen.pngION Setup.png

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-23 08:10 AM

0 Likes
4
6301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-23 08:10 AM

Hello @engenharia_memt ,

 

One thing the config page does not show is the serial settings of each port (8N1). Likely they match but would be the first thing I check. In your text you said port 7702, but I am guessing you meant 7802. Did you confirm that the serial port + goes to + and - to -? Could you share a picture? I assume the ID for Com1 is the device ID you use in ION Setup.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
engenharia_memt
engenharia_memt
Explorer

Posted: ‎2020-07-23 12:11 PM

0 Likes
3
6299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-23 12:11 PM

Hello @Charles_Murison, 

 

I tried to check the serial data bits, parity and stop bits, as you can see in the pictures, but I don't have this option neither in basic options nor in advanced.

Yes, I meant 7802 and checked the wiring + to + and - to - ant the ID was correctly configured in ION Setup.

Anyway, I'm assuming that this might not be the most feasible option and we are thinking about some kind of solution in PME level. If I spend some more energy on that and find any news I will let you know here. 


Thank you!

 

Best Regards,

 

 COMM1-advanced.pngCOMM2-advanced.pngCOMM.png

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-28 11:17 AM

0 Likes
2
6292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-28 11:17 AM

Hello @engenharia_memt ,

 

Does your ION7350 meter have a modem as well as Ethernet? If so this would explain the problem. With a modem, the Com1 is set to modemgate rather than RS-485. If your meter does not have a modem, are you able to talk to the serial port of the Com1 directly with RS-485 converter connected to a computer?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
engenharia_memt
engenharia_memt
Explorer

Posted: ‎2020-07-28 07:36 PM

0 Likes
1
6289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-28 07:36 PM

Hello @Charles_Murison, 

 

oh, right now, I just can't answer your question because the meter itself is isntalled on field and we haven't tested the access via Rs-485 converter, unfortunately. Is there any toher way to check it but by the part number?  One thing that I have checked is that optical port is available, as you can see in attached, and maybe this could "kill" one of the other serial ports. 

Thank you so much for your attention in this case. 

 

 

ION_Setup_Comm.png

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-07-29 06:55 AM

1 Like
0
6288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-29 06:55 AM

Hello @engenharia_memt ,

 

Yes from the serial number I can determine if the meter came with a modem as well as Ethernet. The front optical port does not "kill" other ports. This is a separate port and the meter does not limit the number of serial ports.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore