Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

I have a question regarding the PM8240 IEC61850 Digital Inputs (DI)

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • I have a question regarding the PM8240 IEC61850 Digital Inputs (DI)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
jin1
jin1
Explorer

Posted: ‎2024-08-25 09:34 PM

0 Likes
5
1822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-25 09:34 PM

I have a question regarding the PM8240 IEC61850 Digital Inputs (DI)

Hello,

I have a question regarding the PM8240 IEC61850 Digital Inputs (DI).

When the PANEL ON is activated, the DI State remains in the OFF state, but the Count increments by +1.

  1. Why does the state not change from OFF to ON?
  2. I am using the ICD file PM8000-Onb1-F01_E2V01. Is there a way to customize and retrieve the Count value?

Have a great day!

Labels
  • Labels:
  • ION Setup
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-08-27 09:22 AM

0 Likes
2
1739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-27 09:22 AM

Hello @jin1 

 

For information on how to map custom measurements to GGIO module, please refer to https://product-help.schneider-electric.com/PowerLogic-PM8000/en-us/content/03-communications/mappin....  For explanation on ION Meters and IEC 61850, please refer to https://www.se.com/ca/en/download/document/70022-0125/

As for the digital input, the module setup registers determine what the module will do. Refer to ION Reference for more details on module operation. The Input mode pulse should not prevent the state of the Input module from changing to ON. If you have a transition that is less than a second, unlikely to see the transition in IEC 61850. In situations where input is ON for a longer period of time I would expect to see the state change in IEC 61850

"could the issue be because I'm not using the DO?? "
- Not likely, there are some setup registers in the GGIO module that could change meter's behavior, between reading IO state and control.

"Is there a way to retrieve the count from the DI as a CUS AI?" 
Yes, need to look at mapping additional data to IEC 61850 link above.

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-08-26 09:17 AM

0 Likes
4
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-26 09:17 AM

Hello @jin1 ,

 

The IEC61850 digital input data is updated once a second. If you read the DI state with ION, does the value report ON or OFF. Is the input a pulse or state change?  If input is pulse, the meter's state would change too fast to be read directly through IO state. The input state is not latched. 

 

The ION meter supports some custom analog inputs. You would need to link the count to the custom Analog IEC61850 module and update the CID file as needed. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
jin1
jin1
Explorer

Posted: ‎2024-08-26 08:23 PM . Last Modified: ‎2024-08-26 11:48 PM

0 Likes
3
1765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-26 08:23 PM

Hello,

Thank you so much for your response!

I'm using a program to retrieve IEC61850 values, not ION, and while I'm able to retrieve all the AI values from the PM8240, I'm having trouble with the DI values.

I've had instances where the panel connected to the DI was turned ON and OFF within 1 second, and other times where it was kept ON continuously, but the state always remained OFF.

The count increased by 1 when it went from OFF to ON.
Input mode: pulse
Polarity: Non-Inverting
Debounce: 0.001
Assigned Port: Port S1
EventLog Mode: Log off
S1 state: OFF

The count is increasing, so it seems like the connection is fine. What other aspects should I check? I appreciate your help!

Additionally,

- could the issue be because I'm not using the DO??

- Is there a way to retrieve the count from the DI as a CUS AI? I looked through the Count module and Input module, but I couldn’t find it.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-08-27 09:22 AM

0 Likes
2
1739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-27 09:22 AM

Hello @jin1 

 

For information on how to map custom measurements to GGIO module, please refer to https://product-help.schneider-electric.com/PowerLogic-PM8000/en-us/content/03-communications/mappin....  For explanation on ION Meters and IEC 61850, please refer to https://www.se.com/ca/en/download/document/70022-0125/

As for the digital input, the module setup registers determine what the module will do. Refer to ION Reference for more details on module operation. The Input mode pulse should not prevent the state of the Input module from changing to ON. If you have a transition that is less than a second, unlikely to see the transition in IEC 61850. In situations where input is ON for a longer period of time I would expect to see the state change in IEC 61850

"could the issue be because I'm not using the DO?? "
- Not likely, there are some setup registers in the GGIO module that could change meter's behavior, between reading IO state and control.

"Is there a way to retrieve the count from the DI as a CUS AI?" 
Yes, need to look at mapping additional data to IEC 61850 link above.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
jin1
jin1
Explorer

Posted: ‎2024-08-27 08:30 PM

0 Likes
1
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-27 08:30 PM

I have resolved all the issues, thank you very much.

However, a new problem has arisen. When I press the CID upload or delete buttons, ION SETUP shuts down unexpectedly. I’m not sure why this is happening suddenly.

Is replacing the device the only solution, or could updating from version 4.0.0 to 4.5.0 potentially resolve this issue?

Thank you for your assistance!

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-08-28 02:30 PM

1 Like
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-28 02:30 PM

Hello @jin1 

 

I would not jump to replacing the device just yet. I would work with your local technical support to start a case to troubleshoot this. If possible to include video of what you see and well as provide a copy of the CID file. 

Note that ION Setup is not the only way to upload CID file to the meter. Other sFTP clients can be used if you are in a hurry to deploy.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore