Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to update firmware for multiple PQMs

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How to update firmware for multiple PQMs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Miyai
Miyai
Contributor

Posted: ‎2025-11-13 06:21 PM

0 Likes
12
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-13 06:21 PM

How to update firmware for multiple PQMs

Hello,

 

Normally, when updating the firmware of one PQM (ION9000, PM8000), it is handled using a PC and IONsetup.

 

However, updating the firmware for multiple PQMs takes time.

Therefore, I would like some advice on how to update the firmware for multiple PQMs at once.

 

A customer has asked if there is a way to update the firmware of multiple PQMs in operation at once.

 

 

Regards,

Miyai

Labels
  • Labels:
  • ION9000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-11-14 08:00 AM

0 Likes
0
1929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-14 08:00 AM

Hi @Miyai 

 

ON Setup does not support simultaneous firmware updates. To update multiple meters, either use multiple PCs for parallel updates or use ION Setup’s Device Updater wizard(Tools -> Device Updater), which automates sequential one-by-one updates.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 12
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-11-14 08:00 AM

0 Likes
0
1929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-14 08:00 AM

Hi @Miyai 

 

ON Setup does not support simultaneous firmware updates. To update multiple meters, either use multiple PCs for parallel updates or use ION Setup’s Device Updater wizard(Tools -> Device Updater), which automates sequential one-by-one updates.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2025-11-16 10:22 PM

0 Likes
3
1903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-16 10:22 PM

 

Hi @Mehran_Mehrnia 

 

Thank you for your reply.

 

I wasn’t aware of ION Setup’s Device Updater. Do you have any manuals or documentation for the Device Updater?

 

Is it possible to run the Device Updater with multiple different models specified?
For example, the first device is a PM8240 and the second is an ION9000.

I launched the Device Updater as a trial, and a pop-up indicated that I can use a properly formatted CSV file instead of entering devices manually. Do you have an example CSV file?

 

Regards,
Okada

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-11-17 09:39 AM

1 Like
2
1895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-17 09:39 AM

Hello @T.Okada ,

No there are no official manuals or documentation for the Device Updater. The interface is very simple and not many options available. 

1.) Go to device Updater --> Read pop-up --> Click Next,

2.) Select the checkbox of the specific devices which need to be FW upgraded,

3.) Select the upgrade file individually for the selected devices.

4.) Select device by clicking on row, set the password.

5.) Click Verify

 

 

As for the CSV file, the easiest way to get a file is to make a system with 2-3 devices that match how the system is setup, then select File ->export. Same the file as CSV file. Open the file with either text editor or excel.

 

Use the format in csv file to build out your system.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
T.Okada
T.Okada
Contributor

Posted: ‎2025-11-17 08:35 PM

0 Likes
1
1873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-17 08:35 PM

Hi @Charles_Murison 

 

Thank you for your reply.

 

I used device updater as trial and it works well.

I exported the csv file of the configuration and understand how to describe the file.

 

I have one more question.

When I update the PM8000(example) from ver.2.1.0 to ver.4.5.0, I think I have to run two-step update.

In this case, can I use device updater?

and if I can use device updater, password setting must be standard security?

 

Regards,

Okada

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-11-18 06:56 AM

0 Likes
0
1862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-18 06:56 AM

Hello @T.Okada,

 

PM8000 meters with V2.1.0 firmware can be upgraded to the latest version in  single step. Meters with firmware versions V1.X.X must first be upgraded to V1.4.x then do a 2 stage upgrade to V2.1.0. Contact technical support if you need V1.4.3 as this version is not available online.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2025-11-18 01:45 PM

0 Likes
3
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-18 01:45 PM

The Device Updater in ION Setup still performs the upgrades in a serial manner (FIFO) and does not perform the upgrade in parallel (simultaneously).

In certain situations, this can not be performed in parallel (ex. serial devices connected to a gateway) but for TCP connected devices, there have been separate applications (such as JDX) which launches multiple instances of ION Setup to perform upgrades/template pastes in parallel.

For a small number of upgrades, the ION Setup device upgrader makes sense (and will give an estimate on how long those upgrades might take so you can manage them smartly).  For very large # of upgrades, you might need to contact the US solutions group to see if JDX might be a better solution as ION Setup was not designed for fleet management of devices.

As for multi stage upgrades, the ION Setup Device Updater does not support the ZIP method of upgrades as this requires user input to select which files may or may not be needed on a per device basis.

Reply
Miyai
Miyai
Contributor

Posted: ‎2025-12-02 11:45 PM

0 Likes
2
1676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-02 11:45 PM

Hello @Robert_Lee , @Charles_Murison , @Mehran_Mehrnia 

 

When running Device Updater, does anyone know if there is a way to disable RMP?


I installed the latest IONsetup(v3.2.25317.02) and updated firmware, but I encountered an RMP problem. I've run it several times with the same result.

 

Miyai_0-1764747805637.png

 

 

Best regards,

Miyai

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-12-03 08:02 AM

0 Likes
0
1674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-03 08:02 AM

Hi @Miyai 

 

This error may occur when one or more modules are offline, or when the entire process is affected by an error, resulting in an unsuccessful template upload.

 

If the correct firmware is already installed but the meter is still missing its template, there are two ways to load the template:

Rapid Meter Programming (RMP) – faster method
Non-RMP method

 

In the single upgrade method, it is possible to disable RMP by holding down the <ALT> key and clicking the 'Select' button to send the template file to the meter. However, using the Device Updater method, I am unsure if this option is still available and works.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-12-03 08:29 AM

0 Likes
1
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-03 08:29 AM

Hello @Miyai ,

 

If you  program the meter without using the Device Updater do you get the same error? I do not know of a way to make the device updater not use RMP to program the meter. I would suggest trying to troubleshoot the .dcf file to understand why the error occurs.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Miyai
Miyai
Contributor

Posted: ‎2025-12-04 10:02 PM

0 Likes
0
1643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-04 10:02 PM

Hello @Charles_Murison , @Mehran_Mehrnia 

 

PQM that had RMP issue with Device Updater also had same RMP issue with a regular single update.

As a result, I decided to reinstall the old IONsetup and wait for the issue to be resolved.

 

 

Best regards,

Miyai

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-12-05 08:33 AM

0 Likes
1
1625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-05 08:33 AM

Hi @Miyai 

 

As always, it is recommended to use the latest version of ION Setup. If the Template (DCF) file contains any errors, it will interrupt the template upload, even when using older versions of ION Setup.


As mentioned previously, when performing a single upgrade, you can hold the ALT key and click the Send button to disable RMP downloading on the meter, which helps prevent interruptions during template uploading., however, it is recommended to troubleshoot the .DCF file to identify errors such as offline modules and other related issues.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Miyai
Miyai
Contributor

Posted: ‎2025-12-16 05:30 PM

0 Likes
0
1400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-16 05:30 PM

Hello @Mehran_Mehrnia 

 

Thank you for your support.

 

DCF file uses the standard data included in the firmware information zip(V4.5.0).

PQM settings are standard data with no changes made, so we believe there is little chance of an error in the file.

 

Therefore, we believe that the cause of the error is on the IONsetup software side.

I'll wait for improvements to IONSetup.

 

Best regards,

Miyai

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore