Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84859members
354334posts

How to Configure PM8000 to send emails ?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa315238_brid
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
4
665

How to Configure PM8000 to send emails ?

Dear Gents,

What is the best way to configure PM8000 to send an email in case of an Alarm.

Taking into consideration that i am using PME 8.1

BR,

Sameeh


Accepted Solutions
Adam_Hardman
Commander Commander
Commander

Re: How to Configure PM8000 to send emails ?

Hi Sameeh,

In the PM8000 User Guide under Alarms and alerts there is an overview on the steps you need to take to send an email directly from the PM8000 alerting a user regarding an alarm.

Creating alerts from an ION power meter like the PM8000 is an advanced feature that requires familiarity with ION architecture
and your power system and communications network.

To create an alert, you must configure the Alert module using a configuration tool like Designer in PME or the advanced settings
in ION Setup.

You must also configure your device’s communications as needed to send the alerts, such as configuring your meter’s SMTP settings
and connecting it via Ethernet to an SMTP mail server in order
to send an alert by email.

See the ION meter alerts technical note (70072-0125-02), available from www.schneiderelectric.com, for detailed information on creating and configuring alerts.

Also, see the ION Reference, available from www.schneider-electric.com, for detailed information about the Alert module and its operation.

See Answer In Context

4 Replies 4
Adam_Hardman
Commander Commander
Commander

Re: How to Configure PM8000 to send emails ?

Hi Sameeh,

In the PM8000 User Guide under Alarms and alerts there is an overview on the steps you need to take to send an email directly from the PM8000 alerting a user regarding an alarm.

Creating alerts from an ION power meter like the PM8000 is an advanced feature that requires familiarity with ION architecture
and your power system and communications network.

To create an alert, you must configure the Alert module using a configuration tool like Designer in PME or the advanced settings
in ION Setup.

You must also configure your device’s communications as needed to send the alerts, such as configuring your meter’s SMTP settings
and connecting it via Ethernet to an SMTP mail server in order
to send an alert by email.

See the ION meter alerts technical note (70072-0125-02), available from www.schneiderelectric.com, for detailed information on creating and configuring alerts.

Also, see the ION Reference, available from www.schneider-electric.com, for detailed information about the Alert module and its operation.

sesa315238_brid
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
560

Re: How to Configure PM8000 to send emails ?

Thanks Adam

TruongDoan_ESEC
Ensign
Ensign
0 Likes
1
529

Re: How to Configure PM8000 to send emails ?

Hello all,

 

Has anyone on the forum completed this tag yet?

I am also studying this section, but it has not been done yet.

I am reading the Alert module in the ION reference, but I still cannot configure it.

Hope everyone help.

 

Thank you very much.

Truong Doan

 

 

Charles_Murison
Picard Picard
Picard

Re: How to Configure PM8000 to send emails ?

Hello Truong Doan,

 

I have set this up on numerous meters, from ION 7650 to PM8000 and ION9000. In all cases the setup has been the same

setup smtp server in Ethernet communication module, setup alert module. Can you monitor the traffic from the meter? Could the message be sent from the meter but SMTP server rejects it for some reason? Some SMTP servers will reject messages if to/from address is not in the domain.

L4 Prime for Advanced metering and Utilities