The HDPM6000 is specifically designed to work with Low Voltage Current Transducers (LVCTs) that provide a 250 mV (0.25 V) AC secondary signal at their rated primary current.
As documented in HDPM6000 Series Current Transducer Installation Manual, every CT form factor listed (SUN2, SUN3, SUSF, CTMF, CTTB, etc.) shares: 0.25 V output.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
The HDPM6000 is specifically designed to work with Low Voltage Current Transducers (LVCTs) that provide a 250 mV (0.25 V) AC secondary signal at their rated primary current.
As documented in HDPM6000 Series Current Transducer Installation Manual, every CT form factor listed (SUN2, SUN3, SUSF, CTMF, CTTB, etc.) shares: 0.25 V output.
Best Regards,
-Mehran
L3 Expert Advanced metering