Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

HDPM6000 1-to-1 migration

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • HDPM6000 1-to-1 migration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
TC
TC Explorer
Explorer

Posted: ‎2026-07-14 07:15 PM

0 Likes
2
397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-14 07:15 PM

HDPM6000 1-to-1 migration

Hi Community,

We have a need here to replace one particular set of HDPM6000 with new piece.

 

The question here is:

(1) Existing configuration downloaded from unit with fw 64.0; does it work when uploaded to new unit with fw 66.0 ?

(2) Is there a need to ensure new unit is downgraded first to fw64.0, upload with configuration saved from old unit fw64.0?

(3) Configuration files downloaded will not contain information such as accumulated enegy, demand, etc. Is there a way to port over all these data to new unit? 

 

Labels
  • Labels:
  • HDPM6000
Tags (3)
  • Tags:
  • english
  • HDPM6000
  • HDPM6000R
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-15 09:13 AM . Last Modified: ‎2026-07-15 09:25 AM

0 Likes
0
386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-15 09:13 AM

Hi @TC 

 

Please see my comments below:

1- Yes, but with an important caveat and manual verification step.

While the official user guide(HDPM6000 Configuration Guide) strictly recommends only uploading configuration files (.cfg) between identical firmware versions to prevent setting mismatches,

Mehran_Mehrnia_1-1784131837507.png

 

in practice, you can upload the v64.0 configuration to the v66.0 unit.

The main concern is that because of the firmware gap, certain configuration parameters may not fully or correctly map onto the newer firmware.

In this case, perform the upload and accept any dialog box. Once the upload is complete, manually verify all critical settings via the web user interface to ensure everything applied correctly.

Once you have manually verified the settings on the new v66.0 unit, download a fresh .cfg file from it. This will serve as your new configuration for v66.0, allowing you to bypass the manual verification process if you have to deploy more new units in the future.

 

Or, if the old unit is still operational(although I assume it is not, since it is being replaced), upgrade the old unit's firmware from 64.0 to 66.0. Once completed, download a fresh .cfg file from it. You can then upload this v66.0 configuration file directly to your new unit.

 

2- No, downgrading is not recommended to make it compatible.

We try to avoid FW downgrade whenever possible. Using Method (1) above (uploading the older configuration to the newer firmware and manually verifying the settings) is a much safer, more predictable, and stable path than downgrading the new hardware.

 

3. No, historical energy and demand data cannot be transferred directly to the replacement head unit.

At the device level, Configuration files only contain setup parameters (like communications, mapping, and alarm rules, etc.), they do not capture live accumulator or historical log data. Energy accumulators (kWh) on the HDPM6000 are hardware-managed, read-only registers designed for tamper-proofing. A new head unit will always start accumulating energy and demand from zero.

 

This migration must be managed within your energy management system such as PME. In PME, you can logically link the retired meter's historical databases with the new meter's database or exported from the existing device prior to replacement.

 

Best Regards,

-Mehran

L3 Exert Advanced metering

See Answer In Context

Reply
Replies 2
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-15 09:13 AM . Last Modified: ‎2026-07-15 09:25 AM

0 Likes
0
386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-15 09:13 AM

Hi @TC 

 

Please see my comments below:

1- Yes, but with an important caveat and manual verification step.

While the official user guide(HDPM6000 Configuration Guide) strictly recommends only uploading configuration files (.cfg) between identical firmware versions to prevent setting mismatches,

Mehran_Mehrnia_1-1784131837507.png

 

in practice, you can upload the v64.0 configuration to the v66.0 unit.

The main concern is that because of the firmware gap, certain configuration parameters may not fully or correctly map onto the newer firmware.

In this case, perform the upload and accept any dialog box. Once the upload is complete, manually verify all critical settings via the web user interface to ensure everything applied correctly.

Once you have manually verified the settings on the new v66.0 unit, download a fresh .cfg file from it. This will serve as your new configuration for v66.0, allowing you to bypass the manual verification process if you have to deploy more new units in the future.

 

Or, if the old unit is still operational(although I assume it is not, since it is being replaced), upgrade the old unit's firmware from 64.0 to 66.0. Once completed, download a fresh .cfg file from it. You can then upload this v66.0 configuration file directly to your new unit.

 

2- No, downgrading is not recommended to make it compatible.

We try to avoid FW downgrade whenever possible. Using Method (1) above (uploading the older configuration to the newer firmware and manually verifying the settings) is a much safer, more predictable, and stable path than downgrading the new hardware.

 

3. No, historical energy and demand data cannot be transferred directly to the replacement head unit.

At the device level, Configuration files only contain setup parameters (like communications, mapping, and alarm rules, etc.), they do not capture live accumulator or historical log data. Energy accumulators (kWh) on the HDPM6000 are hardware-managed, read-only registers designed for tamper-proofing. A new head unit will always start accumulating energy and demand from zero.

 

This migration must be managed within your energy management system such as PME. In PME, you can logically link the retired meter's historical databases with the new meter's database or exported from the existing device prior to replacement.

 

Best Regards,

-Mehran

L3 Exert Advanced metering

Reply
TC
TC Explorer
Explorer

Posted: ‎2026-07-16 12:02 AM

0 Likes
0
372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-16 12:02 AM

Thank you @Mehran_Mehrnia . Super Clear.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore