Hi Community,
We have a need here to replace one particular set of HDPM6000 with new piece.
The question here is:
(1) Existing configuration downloaded from unit with fw 64.0; does it work when uploaded to new unit with fw 66.0 ?
(2) Is there a need to ensure new unit is downgraded first to fw64.0, upload with configuration saved from old unit fw64.0?
(3) Configuration files downloaded will not contain information such as accumulated enegy, demand, etc. Is there a way to port over all these data to new unit?
Link copied. Please paste this link to share this article on your social media post.
Hi @TC
Please see my comments below:
1- Yes, but with an important caveat and manual verification step.
While the official user guide(HDPM6000 Configuration Guide) strictly recommends only uploading configuration files (.cfg) between identical firmware versions to prevent setting mismatches,
in practice, you can upload the v64.0 configuration to the v66.0 unit.
The main concern is that because of the firmware gap, certain configuration parameters may not fully or correctly map onto the newer firmware.
In this case, perform the upload and accept any dialog box. Once the upload is complete, manually verify all critical settings via the web user interface to ensure everything applied correctly.
Once you have manually verified the settings on the new v66.0 unit, download a fresh .cfg file from it. This will serve as your new configuration for v66.0, allowing you to bypass the manual verification process if you have to deploy more new units in the future.
Or, if the old unit is still operational(although I assume it is not, since it is being replaced), upgrade the old unit's firmware from 64.0 to 66.0. Once completed, download a fresh .cfg file from it. You can then upload this v66.0 configuration file directly to your new unit.
2- No, downgrading is not recommended to make it compatible.
We try to avoid FW downgrade whenever possible. Using Method (1) above (uploading the older configuration to the newer firmware and manually verifying the settings) is a much safer, more predictable, and stable path than downgrading the new hardware.
At the device level, Configuration files only contain setup parameters (like communications, mapping, and alarm rules, etc.), they do not capture live accumulator or historical log data. Energy accumulators (kWh) on the HDPM6000 are hardware-managed, read-only registers designed for tamper-proofing. A new head unit will always start accumulating energy and demand from zero.
This migration must be managed within your energy management system such as PME. In PME, you can logically link the retired meter's historical databases with the new meter's database or exported from the existing device prior to replacement.
Best Regards,
-Mehran
L3 Exert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @TC
Please see my comments below:
1- Yes, but with an important caveat and manual verification step.
While the official user guide(HDPM6000 Configuration Guide) strictly recommends only uploading configuration files (.cfg) between identical firmware versions to prevent setting mismatches,
in practice, you can upload the v64.0 configuration to the v66.0 unit.
The main concern is that because of the firmware gap, certain configuration parameters may not fully or correctly map onto the newer firmware.
In this case, perform the upload and accept any dialog box. Once the upload is complete, manually verify all critical settings via the web user interface to ensure everything applied correctly.
Once you have manually verified the settings on the new v66.0 unit, download a fresh .cfg file from it. This will serve as your new configuration for v66.0, allowing you to bypass the manual verification process if you have to deploy more new units in the future.
Or, if the old unit is still operational(although I assume it is not, since it is being replaced), upgrade the old unit's firmware from 64.0 to 66.0. Once completed, download a fresh .cfg file from it. You can then upload this v66.0 configuration file directly to your new unit.
2- No, downgrading is not recommended to make it compatible.
We try to avoid FW downgrade whenever possible. Using Method (1) above (uploading the older configuration to the newer firmware and manually verifying the settings) is a much safer, more predictable, and stable path than downgrading the new hardware.
At the device level, Configuration files only contain setup parameters (like communications, mapping, and alarm rules, etc.), they do not capture live accumulator or historical log data. Energy accumulators (kWh) on the HDPM6000 are hardware-managed, read-only registers designed for tamper-proofing. A new head unit will always start accumulating energy and demand from zero.
This migration must be managed within your energy management system such as PME. In PME, you can logically link the retired meter's historical databases with the new meter's database or exported from the existing device prior to replacement.
Best Regards,
-Mehran
L3 Exert Advanced metering