New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Gate drive trip error pcs+
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2026-01-2308:44 AM
Gate drive trip error pcs+
Hi, I hope everyone is having a good day. Recently, I commissioned an Accusine PCS+ filter, but I encountered an error message stating that the contactor has not closed. After investigating further, I found that the gate drive filter has tripped. I believe the contactor issue might be resolved once the gate drive trip is corrected, but I am not sure how to proceed. Any information about this error or guidance on how to address it would be greatly appreciated.
Link copied. Please paste this link to share this article on your social media post.
2026-10-2208:46 PM
Hello Camilo, Sorry, just saw your topic. Yes, your understanding is right. I recommend checking the wiring connections at J17 and J18(white color) on the control board. Please unplug and reconnect the connectors, making sure that they are firmly and securely connected. Then, follow the cables from J17/J18 to the IGBT driver board and check the connections at the three connectors. Please make sure that all connections are secure.
After confirming that all connections are correct and secure, power up the unit again and check whether the problem has been resolved.
If the problem still persists, I recommend swapping the IGBT driver board with the one from another unit to check whether the issue follows the driver board. BRs
Link copied. Please paste this link to share this article on your social media post.
2026-10-2208:46 PM
Hello Camilo, Sorry, just saw your topic. Yes, your understanding is right. I recommend checking the wiring connections at J17 and J18(white color) on the control board. Please unplug and reconnect the connectors, making sure that they are firmly and securely connected. Then, follow the cables from J17/J18 to the IGBT driver board and check the connections at the three connectors. Please make sure that all connections are secure.
After confirming that all connections are correct and secure, power up the unit again and check whether the problem has been resolved.
If the problem still persists, I recommend swapping the IGBT driver board with the one from another unit to check whether the issue follows the driver board. BRs