Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

FTP transfer from ION9000 meter fails almost every time.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: FTP transfer from ION9000 meter fails almost every time.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
572
Mehran_Mehrnia
Mehran_Mehrnia Champion
209
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Paul_Crouch
Paul_Crouch
Explorer

Posted: ‎2025-09-23 11:24 AM

0 Likes
5
2298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-23 11:24 AM

FTP transfer from ION9000 meter fails almost every time.

I have several meters at a site.  I have been trying to download the files using a SFTP software.  I have tried WINSCP and FileZilla and in both cases, I almost always get errors.

 

For the FileZilla; I get an Open Read failure and the transfer fails.

For the WIN SCP I get this error:

General failure (server should provide error description).
Error code: 4
Error message from server:

Common reasons for the Error code 4 are:
- Renaming a file to a name of already existing file.
- Creating a directory that already exists.
- Moving a remote file to a different filesystem (HDD).
- Uploading a file to a full filesystem (HDD).
- Exceeding a user disk quota.

 

This makes using the FTP transfer mostly useless.

 

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-10-15 10:35 AM

0 Likes
0
2057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-15 10:35 AM

Hello @Paul_Crouch ,

 

Have not heard back form you on this topic. If still having trouble please reach out to technical support. Cannot tell from description if something in configuration, system or other. Hopefully the setting suggestions will help your customer.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-09-24 09:09 AM

0 Likes
0
2293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-24 09:09 AM

Hi @Paul_Crouch 

 

Please note that, in ION9000, as of firmware V2.2.1, meter only supports secure file transfer protocol (SFTP). FTP and Telnet protocols are no longer supported.

 

Ensure that the protocol and ports are enabled:

Mehran_Mehrnia_0-1758730152556.png

 

You could check for a direct connection if possible, especially if FTP (on meters with older firmware) or SFTP is being blocked by the network.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-09-24 09:37 AM

0 Likes
0
2289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-24 09:37 AM

Hello @Paul_Crouch ,

 

May need a bit for information about your system. What version of WinSCP do you have? What firmware version?

 

Some settings that may help.

Open Preferences in WinSCP

Under Transfer -> Background
Change the setting Maximum number of transfers at the same time to 1
Uncheck the box for Use multiple connections for single transfer

Under Transfer -> Endurance

Change the setting Enable transfer resume/transfer to temporary filename for to Disable

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Paul_Crouch
Paul_Crouch
Explorer

Posted: ‎2025-09-24 10:24 AM

0 Likes
1
2271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-24 10:24 AM

Hi Charles,

The FW on the all the meters is 2.002, so it is out of date.  Thought I had updated, but had not yet.  

I can download directly from the meter using ION setup.  

I will update the FW on at least on of the meters to see if that helps in any matter.

 

I have changed the WINSCP settings as suggested and will see what happens.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-10-02 09:40 AM

0 Likes
0
2176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-02 09:40 AM

Hello @Paul_Crouch ,

 

Any update about using sFTP?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-10-15 10:35 AM

0 Likes
0
2058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-15 10:35 AM

Hello @Paul_Crouch ,

 

Have not heard back form you on this topic. If still having trouble please reach out to technical support. Cannot tell from description if something in configuration, system or other. Hopefully the setting suggestions will help your customer.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore