Hi everyone.
Can someone explain to me why the 'sequence' is 132 in the Frequency menu in a FDM121?
I have 198 devices all showing this and the costumer thinks it refers to phase rotation because its the same on all the devices. Is 132 equal to a specific amount of waves or is it just the maximum value of a counter.
Hope there is an answer.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
From the photo, the FDM121 is displaying the Frequency measurement screen(you can see the icon which represent a metering screen).
The "132" displayed under sequence is not a frequency value, wave count, or counter value. It is the phase sequence/phase rotation indication reported by the connected Micrologic unit and displayed on the FDM121. In general, 123 corresponds to L1-L2-L3 rotation, while 132 corresponds to L1-L3-L2 rotation.
Since all 198 devices show the same value, this is more likely related to a common system phase rotation or voltage sensing wiring arrangement across the installation. Please verify it for any concerns.
Please note: This forum is primarily intended for Power Meters and Power Quality products. Questions related to circuit breakers, Micrologic trip units, or FDM121 displays are better directed to the Power distribution support community or Schneider Electric technical support team for detailed guidance.
Link copied. Please paste this link to share this article on your social media post.
Hello @Jannik_PS_DK ,
The FDM121 is a display that is connected to a breaker. There are a few different types of breaker that the display supports. Would need to know what break the display is connected to. With that info we can move the post to the correct team.
I do not know the breakers or the display so I cannot not for sure, however, I think sequency does relate to the phase order (123, 132). I don't know if this is a setting in the breaker or just a reading.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
From the photo, the FDM121 is displaying the Frequency measurement screen(you can see the icon which represent a metering screen).
The "132" displayed under sequence is not a frequency value, wave count, or counter value. It is the phase sequence/phase rotation indication reported by the connected Micrologic unit and displayed on the FDM121. In general, 123 corresponds to L1-L2-L3 rotation, while 132 corresponds to L1-L3-L2 rotation.
Since all 198 devices show the same value, this is more likely related to a common system phase rotation or voltage sensing wiring arrangement across the installation. Please verify it for any concerns.
Please note: This forum is primarily intended for Power Meters and Power Quality products. Questions related to circuit breakers, Micrologic trip units, or FDM121 displays are better directed to the Power distribution support community or Schneider Electric technical support team for detailed guidance.
Link copied. Please paste this link to share this article on your social media post.
The FDM121 is connected to NSX400 with a Micrologic 7.3E-AL ETU.
Further investigation was done and the AP told me that they changed the phase order on the MV side. Now they are in the process of changing the settings through out the system.
I have reposted in the Power Distribution community. Thanks for all the help.