Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

FDM121 Frequency menu

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • FDM121 Frequency menu
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Jannik_PS_DK
Jannik_PS_DK Explorer
Explorer

Posted: ‎2026-09-04 05:14 AM

0 Likes
3
346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-04 05:14 AM

FDM121 Frequency menu

Hi everyone.

Can someone explain to me why the 'sequence' is 132 in the Frequency menu in a FDM121?

I have 198 devices all showing this and the costumer thinks it refers to phase rotation because its the same on all the devices. Is 132 equal to a specific amount of waves or is it just the maximum value of a counter.

Hope there is an answer.

Thanks.Image (11).jpg

Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2026-09-07 02:24 AM

1 Like
0
311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-07 02:24 AM

Hi @Jannik_PS_DK 

From the photo, the FDM121 is displaying the Frequency measurement screen(you can see the icon which represent a metering screen).
The "132" displayed under sequence is not a frequency value, wave count, or counter value. It is the phase sequence/phase rotation indication reported by the connected Micrologic unit and displayed on the FDM121. In general, 123 corresponds to L1-L2-L3 rotation, while 132 corresponds to L1-L3-L2 rotation.

Since all 198 devices show the same value, this is more likely related to a common system phase rotation or voltage sensing wiring arrangement across the installation. Please verify it for any concerns.

 

Please note: This forum is primarily intended for Power Meters and Power Quality products. Questions related to circuit breakers, Micrologic trip units, or FDM121 displays are better directed to the Power distribution support community or Schneider Electric technical support team for detailed guidance.

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-09-04 08:39 AM

1 Like
0
339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-04 08:39 AM

Hello @Jannik_PS_DK ,

 

The FDM121 is a display that is connected to a breaker. There are a few different types of breaker that the display supports. Would need to know what break the display is connected to. With that info we can move the post to the correct team.

 

I do not know the breakers or the display so I cannot not for sure, however, I think sequency does relate to the phase order (123, 132). I don't know if this is a setting in the breaker or just a reading.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2026-09-07 02:24 AM

1 Like
0
311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-07 02:24 AM

Hi @Jannik_PS_DK 

From the photo, the FDM121 is displaying the Frequency measurement screen(you can see the icon which represent a metering screen).
The "132" displayed under sequence is not a frequency value, wave count, or counter value. It is the phase sequence/phase rotation indication reported by the connected Micrologic unit and displayed on the FDM121. In general, 123 corresponds to L1-L2-L3 rotation, while 132 corresponds to L1-L3-L2 rotation.

Since all 198 devices show the same value, this is more likely related to a common system phase rotation or voltage sensing wiring arrangement across the installation. Please verify it for any concerns.

 

Please note: This forum is primarily intended for Power Meters and Power Quality products. Questions related to circuit breakers, Micrologic trip units, or FDM121 displays are better directed to the Power distribution support community or Schneider Electric technical support team for detailed guidance.

Reply
Jannik_PS_DK
Jannik_PS_DK Explorer
Explorer

Posted: ‎2026-09-08 12:21 AM

1 Like
0
284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-08 12:21 AM

The FDM121 is connected to NSX400 with a Micrologic 7.3E-AL ETU.

Further investigation was done and the AP told me that they changed the phase order on the MV side. Now they are in the process of changing the settings through out the system. 

I have reposted in the Power Distribution community. Thanks for all the help.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore