Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Device Information Serial number not showing

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Device Information Serial number not showing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
195
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EasyLogic PM2000 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Bryanbyte
Bryanbyte
Contributor

Posted: ‎2026-04-08 03:29 AM

0 Likes
4
508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-08 03:29 AM

Device Information Serial number not showing

Hi,

I would like to ask for assistance regarding device identification in ION Setup.

I am currently scanning multiple Schneider PM2200 series power meters (specifically PM2230) via Modbus in ION Setup. All devices are successfully detected, and communication is confirmed (I can read measurement data without issue).

However, I noticed that for some meters, the Device Information (e.g., serial number) is not displayed during the scan, while other meters of the same model do show complete information.

Details:

  • Same model: PM2230
  • Communication: Modbus RTU (working)
  • ION Setup device type: correctly selected based on field device
  • Using Modscan, I can manually read the serial number (e.g., register 130) from the affected meters
  • Firmware example: OS Firmware 1.4.0, RS Firmware 1.0.1

Based on testing, it seems the serial number exists but is not being interpreted/displayed correctly in ION Setup.

My questions:

Bryanbyte_0-1775644088576.png

 

  1. Are there known differences in firmware or Modbus register formatting (e.g., word/byte order) that affect how ION Setup reads device identity?
  2. Does ION Setup rely on a fixed device profile that may not match certain firmware versions?
  3. Is there a recommended way to ensure full device information (serial number) is displayed consistently across all meters?

Any guidance or clarification would be greatly appreciated.

Thank you.

  • Thumbnail of EasyLogic PM2000 series
    Schneider Electric
    EasyLogic PM2000 series
View products (1)
Labels
  • Labels:
  • ION Setup
  • PM3000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2026-05-05 09:41 AM

0 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-05 09:41 AM

Yes, that ION Setup is 4.5 years old (late 2021 based on that build #).

I would also confirm using the integrated Modbus Tester UI in ION Setup (click on the Troubleshooting tab you see in your screenshot) and use the Modbus Ident (0x2B) and Read Holding Registers (0x03) to confirm the SN# register is being read correctly.


See Answer In Context

Reply
Replies 4
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2026-04-08 09:08 PM

0 Likes
1
484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-08 09:08 PM

Hi @Bryanbyte Please share some more details like ION setup version you've used, affected meter's S/N & FW version as well as some unaffected meter's S/N & FW version.

Reply
Bryanbyte
Bryanbyte
Contributor

Posted: ‎2026-04-08 09:39 PM

0 Likes
0
481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-08 09:39 PM

Here is one of the Meters I have in my shelf I encounter having same issue. I have installed another 10 at the site but I can't give its SN.

Screenshot 2026-04-08 122716.png

Bryanbyte_0-1775709400213.png

 

 

Reply
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2026-04-15 09:55 PM

0 Likes
0
405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-15 09:55 PM

Hello @Bryanbyte With the meters in our lab, we are not getting such issues. Please try upgrading the ION setup version and see if it helps.

 

Hi @Robert_Lee Please check and answer for this query.

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2026-05-05 09:41 AM

0 Likes
0
278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-05 09:41 AM

Yes, that ION Setup is 4.5 years old (late 2021 based on that build #).

I would also confirm using the integrated Modbus Tester UI in ION Setup (click on the Troubleshooting tab you see in your screenshot) and use the Modbus Ident (0x2B) and Read Holding Registers (0x03) to confirm the SN# register is being read correctly.


Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore