Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Custom framework migration (ION9000)

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Custom framework migration (ION9000)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
TC
TC Explorer
Explorer

Posted: ‎2026-03-25 06:05 PM

0 Likes
5
413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-25 06:05 PM

Custom framework migration (ION9000)

Hi, we have multiple units of ION9000 with hyper scaler DC, all of which with fw 3.1, and heavily customized framework. A lot of modules (modbus master device 1-49, modbus master map 1-13, display 9-17, convert, modbus slave, aritmetic, pulse merge, AND/OR, data recorder, etc)

 

Now, there is a need to upgrade firmware to latest 4.6 (or 4.7 we are considering).

The question is how to do it "most efficiently" and "error free".

 

Lead to believe the "error free" method is per below, which is very crumble some, and needing advice how can we simply?

 

(1) Download from site each ION9k existing dcf file using ION Setup

(2) Back in office, find a unit of ION9k (temp_ION9k_v3.1) ;fw 3.1, which we struggled to get one as most of ours in lab are already v4.x

(3) Using IONsetup, load the dcf file taken from site to the temp_ION9k_v3.1.

(4) connect temp_ION9k_v3.1 to PME instance and open Designer

(5) Locate added module and save it as "added_module.fwn"

(6) find yet another ION9k (temp_ION9k_v4.6); which we have to find a way to locate second piece.

(7) connect temp_ION9k_v4.6 to PME instance and open Designer

(8) paste "added_module.fwn" into factory template (and lots of validations to make sure modules are integrated properly, not overriding factory template modules)

(9) from IONSetup, download dcf file and save as "dcf_v4.6__updated_with_added_module" 

(10) bring the dcf file generated from step 9 to site, load into ION9k after it is updated to 4.6

 

Labels
  • Labels:
  • ION Setup
  • ION9000
Tags (2)
  • Tags:
  • custom framework migration
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RobGraham
RobGraham Champion
Champion

Posted: ‎2026-03-26 04:11 AM

0 Likes
1
406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-26 04:11 AM

This is a good idea to verify with one meter, as changes to the supported modules do happen occasionally.  However, in theory, you should be able to simply download the .dcf, upgrade the firmware, then reload the .dcf in one shot.  

 

For your information, modern ION Setup can also load full .fwn files to a meter instead of a .dcf if it's more convenient.  Just select all modules in Designer and copy to framework.  I think it can also lock-paste partial .fwn files, but I haven't worked with that myself.

See Answer In Context

Reply
Replies 5
RobGraham
RobGraham Champion
Champion

Posted: ‎2026-03-26 04:11 AM

0 Likes
1
407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-26 04:11 AM

This is a good idea to verify with one meter, as changes to the supported modules do happen occasionally.  However, in theory, you should be able to simply download the .dcf, upgrade the firmware, then reload the .dcf in one shot.  

 

For your information, modern ION Setup can also load full .fwn files to a meter instead of a .dcf if it's more convenient.  Just select all modules in Designer and copy to framework.  I think it can also lock-paste partial .fwn files, but I haven't worked with that myself.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-03-26 07:08 AM . Last Modified: ‎2026-03-26 07:08 AM

0 Likes
0
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-26 07:08 AM

Hello,

 

If there were any changes to the modules supported you would see when doing a framework paste.

 

One suggestion would be sure that you maintain external inputs when saving the framelet. The steps as described are the steps I would do myself.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2026-03-26 09:08 AM

0 Likes
0
398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-26 09:08 AM

Please let us know how this goes - one additional thought is to maintain in the fwn format (as ION Setup supports fwn) and this opens up maintaining your framelet as a partial framework (ie. group in a customer folder and save just that folder) that can be applied to future factory frameworks in Designer.  

Reply
TC
TC Explorer
Explorer

Posted: ‎2026-03-26 10:38 PM

0 Likes
0
390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-26 10:38 PM

Thank you @RobGraham @Charles_Murison @Tom_Stevenson for feedback. 

Now I am convinced I am not alone.

 

The optimization I gathered, will be on step 9 and 10, where after pasting the custom framework in Designer, I will save as .fwn file, and integrate it into single fw4.7 update zip package. For on-site one-time upgrade via IONSetup.

 

Any indication whether this kind of migration work can be made easier/automated near future? Via IONSetup maybe? Removing the need of very back office support.

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2026-03-27 12:39 PM

0 Likes
0
360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-27 12:39 PM

Hi TC - you could streamline by doing a partial framework paste from Designer with your custom framelet vs. maintaining a complete template.  This would cut out steps from your process and your framelet becomes less subject to factory framework changes.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore