Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84306members
353462posts

Confirmation of system architecture

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

dario_andl_nabl
Lieutenant JG
Lieutenant JG
0 Likes
1
379

Confirmation of system architecture

Hi,

 

can someone confirm/correct my block scheme from attachement?

 

I never had PME project with Sepam's and ION devices so I am not familiar with connecting them and using ION 7650 as gateway for 3rd party Modbus RTU devices.

 

Thanks in advance!

 

Regards,

 

Dario

Attachments
1 Reply 1
Philippe_Morel
Commander Commander
Commander

Re: Confirmation of system architecture

Looks OK to me.

For each Sepam you need an external module (ACE850) for direct connection to Ethernet.

You can also use one or two gateways with the modules ACE949-2 (RS485), which I believe is a lot cheaper.

But that's just my two cents...