Coincident values with demand values

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa125036_brid
Lieutenant Lieutenant
Lieutenant
0 Likes
2
211

Coincident values with demand values

Hi,

 

please advise if we can create a custom calculation, to find out the coincident values for power and PF, for the corresponding demand values in ION7650 / ION9000 meters?

example:

KW Coincident with peak KVA and KVAR demand.

 

Thanks

Gautam


Accepted Solutions
Charles_Murison
Picard Picard
Picard

Re: Coincident values with demand values

Are you looking to store the value of kVA and kVAR at the time of peak kW?

 

If so, could the following work for you?

Create 2 store modules, one for kVA, one for kVAR, link the inputs to the desired measurement.

Connect the kW maximum module's trigger output to store module's store input.

L4 Prime for Advanced metering and Utilities

See Answer In Context

2 Replies 2
Charles_Murison
Picard Picard
Picard

Re: Coincident values with demand values

Are you looking to store the value of kVA and kVAR at the time of peak kW?

 

If so, could the following work for you?

Create 2 store modules, one for kVA, one for kVAR, link the inputs to the desired measurement.

Connect the kW maximum module's trigger output to store module's store input.

L4 Prime for Advanced metering and Utilities
sesa125036_brid
Lieutenant Lieutenant
Lieutenant

Re: Coincident values with demand values

Thanks