I have an additional question.
In the 208V 3-phase, 3-wire system mentioned above, if UL certification is not required,
can the A9MEM1560 be used for Power Tag Unit 1 and the A9MEM1580 for Power Tag Unit 2?
I would appreciate your help. Thank you.
Link copied. Please paste this link to share this article on your social media post.
Hi @Kwon,
It is possible to use the A9MEM1560 in a 2-phase application if no neutral is available and the load is supplied only between phases. The line-to-line voltage (VLL) must be within the specified operating range of 200-240 V AC ±20%.
The PLTQO302P is designed specifically for Square D breakers, so it may not be compatible with other breaker types out of the box.
Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hi Kwon
As per my understanding and findings :
Link copied. Please paste this link to share this article on your social media post.
Thank you for the quick reply.
In that case, this means that the only PowerTag product compatible with the "PowerTag Unit 1" (208V single-phase L-L) shown in the photo above is Product PLTQO302P, which is designed for QO-type circuit breakers.
However, since Fuji Electric circuit breakers are currently being used on-site, it is difficult to propose PowerTag.
Is there any way to propose a different product from the PowerTag lineup?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Hi @Kwon,
It is possible to use the A9MEM1560 in a 2-phase application if no neutral is available and the load is supplied only between phases. The line-to-line voltage (VLL) must be within the specified operating range of 200-240 V AC ±20%.
The PLTQO302P is designed specifically for Square D breakers, so it may not be compatible with other breaker types out of the box.
Regards,
JD