Anyone implementing IEEE 519-2014 Short Time Harmonic Values in ION modules?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa252887_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
3
303

Anyone implementing IEEE 519-2014 Short Time Harmonic Values in ION modules?

Please refer to the article for more details. Computing IEEE 519-2014 Short Time Harmonic ValuesCodeCogsEqn.png?t=1455891388187&width=154

Not sure if PM8000 is capable of delivering this value.

Jiafeng Huang

@Ken Hsu

@Charles Wu

3 Replies 3
Kevin_Huang
Spock Spock
Spock
0 Likes
0
264

Re: Anyone implementing IEEE 519-2014 Short Time Harmonic Values in ION modules?

Jim Bradley



Kevin Huang
PME Global Offer Manager

Click here to learn more on how PME helps you improve electrical safety, power reliability, operation efficiency and regulation compliance of your facility.
Kevin_Huang
Spock Spock
Spock

Re: Anyone implementing IEEE 519-2014 Short Time Harmonic Values in ION modules?

The current 519 framework on PM8000 is based on IEEE 519 1992 so it doesn't have the calculation you show.  It is possible to implement IEEE 519 2014 edition but it has not been prioritized into our framework development yet.



Kevin Huang
PME Global Offer Manager

Click here to learn more on how PME helps you improve electrical safety, power reliability, operation efficiency and regulation compliance of your facility.
DanL
Commander Commander
Commander

Re: Anyone implementing IEEE 519-2014 Short Time Harmonic Values in ION modules?

Yes.

The "very short time or 3 seconds" aggregation interval from IEEE519 is equivalent to the 150/180 cycle aggregation interval specified in IEC61000-4-30.

The “short time or 10 minutes" aggregation interval from IEEE519 is equivalent to the 10minute aggregation interval specified in IEC61000-4-30.

Both of these quantities are available for measurment (Harmonics Measurement Module) and compliance monitoring (Harmonics Evaluation Module) in the PM8000.