Accusine PCSn - Minimum Current Transformer Primary Current?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa108084_brid
Lieutenant JG Lieutenant JG
Lieutenant JG

Accusine PCSn - Minimum Current Transformer Primary Current?

Good day

 

Is the minimum primary current rating for the CT has to be 100A?

My installation incomer is only 32A.


TQ
 

Attachments
1 Reply 1
LazCM_175878
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: Accusine PCSn - Minimum Current Transformer Primary Current?

Hi,

yes CT sensors  must be selected according to SE recommendation:
• 5 A or 1 A secondary
• 100A to 10,000A primary rating
• 50/60 Hz or 400 Hz Rated
• Type 1 accuracy
• The CT primary current rating must exceed the maximum load current where they
are installed!

LCM