Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

AccuSine RMS current switching frequency

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: AccuSine RMS current switching frequency
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
573
Mehran_Mehrnia
Mehran_Mehrnia Champion
210
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sebastian_P
Sebastian_P
Contributor

Posted: ‎2025-10-30 09:08 AM

0 Likes
4
890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-30 09:08 AM

AccuSine RMS current switching frequency

Hello

 

I have read something about three types of switching frequency called r1, r2 and r3 (see picture below) Can anyone tell me the meaning of them?

 

Sebastian_P_0-1761840167891.png

Thanks. 

  • Thumbnail of AccuSine PCS+
    PowerLogic
    AccuSine PCS+
View products (1)
Labels
  • Labels:
  • Power Quality
Tags (2)
  • Tags:
  • english
  • spanish
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Yan_Zhang
Yan_Zhang Troubleshooter
Troubleshooter

Posted: ‎2025-11-24 05:04 PM

0 Likes
1
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-24 05:04 PM

Hello @Sebastian_P 

Apologies for my delay reply.

We divide 3 ranges is just for help us to identify what cause the current flow into filter increase.

e.g. if r1(lower freq than r2) tripped, that would caused by some passive reactive power resonance happen.

if r2 tripped, then maybe AHF might involved resonance with some other units, and for r3, some high frequency source should be pay attention...

This "filter diagnostic" provides  a general direction for the fault.

Best Regards

See Answer In Context

Reply
Sebastian_P
Sebastian_P
Contributor

Posted: ‎2025-11-27 01:53 PM

1 Like
0
619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-27 01:53 PM

Hello @Yan_Zhang 

 

Thanks for the answer. Now the concept is clear for me. You have been very helpful 

 

Best Regards

See Answer In Context

Reply
Replies 4
Yan_Zhang
Yan_Zhang Troubleshooter
Troubleshooter

Posted: ‎2025-10-30 09:37 PM

1 Like
1
874
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-30 09:37 PM

Hello Sebastian,

Good day!
r1: the frequency range which lower than IGBT switching frequency.

r2: the frequency range which around IGBT switching frequency(15kHz~21kHz).

r3: the frequency range which higher than IGBT switching frequency.

The values in the table represents the RMS value current or voltage in according frequency range.

BRs

Reply
Sebastian_P
Sebastian_P
Contributor

Posted: ‎2025-11-03 04:07 AM

0 Likes
0
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-03 04:07 AM

Hello @Yan_Zhang 

 

Thanks for the answer. Im sorry if I don´t understand completly the concept, but I know that the AccuSine has one switching frecuency privided for their IGBT. So why there is three ranges called r1, r2 y r3? What is the relationship between electronics IGBT switching frecuency and r1, r2, r3? Could be that these ranges are separated by software and represents differents groups of Harmonics to compensate? 

 

Thanks again.

Reply
Yan_Zhang
Yan_Zhang Troubleshooter
Troubleshooter

Posted: ‎2025-11-24 05:04 PM

0 Likes
1
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-24 05:04 PM

Hello @Sebastian_P 

Apologies for my delay reply.

We divide 3 ranges is just for help us to identify what cause the current flow into filter increase.

e.g. if r1(lower freq than r2) tripped, that would caused by some passive reactive power resonance happen.

if r2 tripped, then maybe AHF might involved resonance with some other units, and for r3, some high frequency source should be pay attention...

This "filter diagnostic" provides  a general direction for the fault.

Best Regards

Reply
Sebastian_P
Sebastian_P
Contributor

Posted: ‎2025-11-27 01:53 PM

1 Like
0
620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-27 01:53 PM

Hello @Yan_Zhang 

 

Thanks for the answer. Now the concept is clear for me. You have been very helpful 

 

Best Regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore