Hi experts,
Recently I have T&C 2 AHF AccuSine PCS+ 300A. But just 1 of them can be ready for T&C and 1 can not. They all have the same condition Linr Voltage, DC bus top, DC bus bottom, all temperature value is fine. We received an alarm on HMI: “Contactor not closed”. And Contactor State “Gate drive not ready”. I log in account, tap reset button that is beside the contactor state text box display. But nothing happens. This alarm still display. I hope I can receive your help
Link copied. Please paste this link to share this article on your social media post.
Hello Long,
Good day!
I recommend checking the wiring connections at J17 and J18(white color) on the control board. Please unplug and reconnect the connectors, making sure that they are firmly and securely connected.
Then, follow the cables from J17/J18 to the IGBT driver board and check the connections at the three J408 connectors. Please make sure that all connections are secure.
After confirming that all connections are correct and secure, power up the unit again and check whether the problem has been resolved.
If the problem still persists, I recommend swapping the IGBT driver board with the one from another unit to check whether the issue follows the driver board.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Hello @long28082002 ,
Looking at other topics on AccuSine products, I recommend you contact your local Customer Care Center (CCC) to start a case to trouble shoot.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello Long,
Good day!
I recommend checking the wiring connections at J17 and J18(white color) on the control board. Please unplug and reconnect the connectors, making sure that they are firmly and securely connected.
Then, follow the cables from J17/J18 to the IGBT driver board and check the connections at the three J408 connectors. Please make sure that all connections are secure.
After confirming that all connections are correct and secure, power up the unit again and check whether the problem has been resolved.
If the problem still persists, I recommend swapping the IGBT driver board with the one from another unit to check whether the issue follows the driver board.
Best Regards