Continue
  • My Subscriptions
  • Events
PM5110 reading internal registers
Machine and Motion Control Forum
Support forum for Machine and Motion Control solutions, including Lexium MC12 and robotics, PacDrive, Modicon PLCs and I/Os, EcoStruxure Machine Expert Twin, … - from design, implementation to troubleshooting and more, by Schneider Electric
  • Industrial Automation
  • Re: PM5110 reading internal registers
Bastian_Schmitz
Bastian_Schmitz Champion
9
FernandoRodrigues
FernandoRodrigues Troubleshooter
8
Francesco_Begnoni
Francesco_Begnoni Troubleshooter
6
Back to Machine and Motion Control Forum
kasmic_mike
kasmic_mike
Contributor
Posted: ‎2022-10-31 03:42 AM
5616
@LeTomas,@FedericoM,@Bastian_Schmitz
Has any one succeeded on reading  registers 3020,3000 for PM5110 with ESME Using M241 PLC MODBUS.
i configured my M241 SL2.
The data access type set to function code 03 for read only
1.The master MODBUS IO SCANNER is showing running.
2.the generic bus shows an orange triangle
When I set my data access type to function code 16 the orange triangle turn to running and bus runs
but I still could not see any voltage values reading.
 see attachment.
thanks
KASMIC
  • Modicon M2xx
LeTomas
LeTomas Mentor
Mentor
Posted: ‎2022-10-31 03:58 AM
5609
Hi @kasmic_mike
I have played with one of the PM5xxx in our lab with the M262.
Please check the example project in the next link:
https://schneider-electric.box.com/s/lhuus6bvlcivkmkbxvqsn9fc26c26ffa
In the project you will see that I have used the FC03 along with some function that i have done to convert the 2 word to real.
Check if this example works on your side with the M241, then change/add another channel to access to the registers that you want and be careful with the length of the variables.
Best regards,
Marian_Pavlik
Marian_Pavlik Troubleshooter
Troubleshooter
Posted: ‎2022-11-02 07:44 AM
In response to kasmic_mike
5588
there are to tricks to reach good result.
From modbus.org >
Registers are addressed starting at zero. Therefore register numbered 1 is addressed as 0.
To read voltage registers starting from register 3020 via M241 Modbus IO scanner you need to ask for number of register minus one to ask register address so 3019 = 16#0BCB.
The reason of your error is that Voltage value is FLOAT32 what is in 2 registers.
If Modbus request is moved by one register you ask not valid data and get Exception answer.
The second is that PM5000 and M241 use different word order in FLOAT32 so you have to swap WORDs to get correct result.
To that reason you get nice example and function FC_FLOAT32_REAL from Leandro Tomas Ahumada.
kasmic_mike
kasmic_mike
Contributor
Posted: ‎2022-11-03 08:25 AM
In response to Marian_Pavlik
thanks @Marian_Pavlik @LeTomas
your guidance was really helpful.  I was able to read register for voltage, I used the excel float32 to real at above link to confirm reading.https://ckm-content.se.com/ckmContent/sfc/servlet.shepherd/document/download/0691H00000EF0hoQAD
Am now working on the swapping WORDs. then display them on HMI
KASMIC
Replies 5
LeTomas
LeTomas Mentor
Mentor
5609
Hi @kasmic_mike
Best regards,
kasmic_mike
kasmic_mike
Contributor
Posted: ‎2022-10-31 05:05 AM
In response to LeTomas
5604
thanks i am going to check through the example critically. however if you have some examples with LD blocks or literature it will guide  me through. because am not so good with the structured programme.
KASMIC
Marian_Pavlik
Troubleshooter
5588
From modbus.org >
kasmic_mike
kasmic_mike
Contributor
KASMIC
jhonut
jhonut
Explorer
Posted: ‎2024-04-26 12:41 AM
Hi!
Very useful the excel. Do you have a version of it for reading some energy (4 registers) parameters?
Many thanks in advance!
