Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

M221 LOGIN FAIL

Machine Automation Forum

A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Industrial Automation
  • Machine Automation Forum
  • M221 LOGIN FAIL
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Lt. Commander FedericoM Lt. Commander
30
Bastian_Schmitz
Commander Bastian_Schmitz Commander
30
LeTomas
Lt. Commander LeTomas Lt. Commander
12
Ralf
Lieutenant JG Ralf Lieutenant JG
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Machine Automation Forum
Ravi_Prabhat
Crewman Ravi_Prabhat
Crewman

Posted: ‎2021-08-05 04:50 AM

0 Likes
4
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-08-05 04:50 AM

M221 LOGIN FAIL

We have bought a new PLC (Model: TM221M16T, SV:1.10). We have connected the PLC to laptop with Schneider mini USB cable TQBMXXCAUSBH045. Ecostruxure software shows M221(USB) in local devices. But every time I try to login the PLC with ecostruxure software, it fails to login with advisory "Communication detection error, Verify USB cable, mod-bus driver parameters, controller connection, power supply."

Capture0.JPGCapture.JPG

Labels
  • Labels:
  • Modicon M2xx
  • Tags:
  • ecostruxure
  • english
  • m221
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Bastian_Schmitz
Commander Bastian_Schmitz Commander
Commander

Posted: ‎2021-08-15 11:32 PM

1 Like
2
1103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-08-15 11:32 PM

Hello,

Could you connect to an other TM221 controller?

Did you try to uninstall the USB driver and to reinstall ESME Basic?

For me it looks like an driver issue. 

The connection should be possible through Mini USB it is not neccassary to supply the controler additional via 24V DC.

Please check if the drive would be recognized corectly at the windows device manager

m221 treiber.PNG

  • Tags:
  • english
Reply
Ravi_Prabhat
Crewman Ravi_Prabhat
Crewman

Posted: ‎2021-08-17 03:07 AM

In response to Bastian_Schmitz
0 Likes
0
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-08-17 03:07 AM

The TM221 Controller is brand new. I don't have any other.

I tried MachineExpertBasic_V1.2_build65304  but still, not able to login. I reinstalled USB driver also, SchneiderPLCUSBDriverSuite V14.12.0.0. When I connect the controller, device manager shows M221 Controller. But still ecostruxure cannot login.Screenshot 2021-08-17 140626.jpg 

  • Tags:
  • english
Reply
Jayce83
Jayce83
Cadet

Posted: ‎2022-02-17 06:15 AM

In response to Bastian_Schmitz
0 Likes
0
761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-17 06:15 AM

I have a plc TM200C32R. Try to connect it to my computer via mini-usb.. The computer detect the controller.,But i can't login,"communication detected error," something like that..But when i try to connect to other plc like TM200C24, no problem at all,i can connect and login to it..im using machine expert basic v1.2.. Anyone have an idea about it, why it can't connect to TM200C32R? 

  • Tags:
  • english
Reply
Asmawan_Putra
Crewman Asmawan_Putra
Crewman

Posted: ‎2022-02-22 04:32 AM

0 Likes
0
752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-22 04:32 AM

To check if the problem comes from electrical installation:

- unplug PLC power

- unplug laptop charger

- power PLC only by the aptop via USB cable

- try login again

It usually works for me. Please update me if it solves your problem. I want to know if it works for others.

  • Tags:
  • english
Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc