Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82566members
350187posts

RFA file import to Revit

LayoutFAST User Group Forum

The LayoutFAST User Group is a place where Specifiers, Contractors, and Panel Builders share their User experience with the tool and ask Schneider Electric experts questions to solve their issues.

Solved
SophieMBrause
Crewman
Crewman
0 Likes
1
446

RFA file import to Revit

After creating a layout using the Web-based LayoutFAST and saving the .rfa file to my computer, how do I import it into room layout? I tried the below steps without success on a low voltage transformer

Tags (1)

Accepted Solutions
FelixRamos
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
405

Re: RFA file import to Revit

Hi Sophie, 

 

If a product is configured in LayoutFAST web, simply download that file to your local computer.  Select the file locally and drag and drop it into your Revit model. 

 

Another option is to:

 

  1. Download the RFA,
  2. Open the Revit project,
  3. Click the Load Family button
  4. Browse to the downloaded RFA,
  5. Place the RFA using the Electrical Equipment tool.  There is no need to open the downloaded RFA (that was an old workflow for switchboards and other lineup products that is no longer necessary)

Thanks for your inquiry!  We hope this helps. 

 

Felix 

See Answer In Context

Tags (1)
1 Reply 1
FelixRamos
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
406

Re: RFA file import to Revit

Hi Sophie, 

 

If a product is configured in LayoutFAST web, simply download that file to your local computer.  Select the file locally and drag and drop it into your Revit model. 

 

Another option is to:

 

  1. Download the RFA,
  2. Open the Revit project,
  3. Click the Load Family button
  4. Browse to the downloaded RFA,
  5. Place the RFA using the Electrical Equipment tool.  There is no need to open the downloaded RFA (that was an old workflow for switchboards and other lineup products that is no longer necessary)

Thanks for your inquiry!  We hope this helps. 

 

Felix 