Posted: 2019-09-09 11:31 PM . Last Modified: 2020-12-02 04:31 AM
Hi All,
I have a scenario in which an STR-150 thermostat and a return sensor are to be connected to a Xenta-122FC. I need to run the Xenta controller based on the return sensor temperature value and setpoint to be given from server. And have to export the temperature & setpoint values from STR-150 to other controller(to be used for other purpose). Does anyone know how to achieve this? Which of the Xenta terminals the thermostat and return sensor should be connected? How should be the bindings be done?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-10 04:46 AM
Hello @digvijay , welcome on Exchange community. I add @MikaelKrantz to the thread as he may be able to help you with your issue.
PS: do not hesitate to use the search bar with key words to check if your issue was not already discussed somewhere in the community 😉
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-10 06:58 AM
The TAC Xenta 122-FC device has to be configured with the ZBuilder tool, that is an LNS PlugIn software.
Here you can select what input you should use for the temp, and under Configuration tab, Application, Special Functions, there is a checkbox for selecting Do not use space temperature from STR150.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-10 07:24 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-10 07:36 AM
Not from the sensor, but from the controller.
nvoSpaceTemp
nvoEffectSetpt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-11 10:33 PM
Let me check on the site for the values on these NVOs and get back to you. Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-26 12:06 AM
Is there any option for the selection of either STR-150 or temperature sensor once controller is added under SBO under these sub folder as my previous selection in this controller on return sensor now I want to replace it with STR-150 and I don't have LNS or Tac vista.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-26 12:53 AM
What type of controller du you have?
STR150 only talk to the TAC Xenta 100 series.
Or, do you think about STR350, which are using SNVT?
Link copied. Please paste this link to share this article on your social media post.