Posted: 2025-04-08 10:37 PM
Hi,
We recently installed the new SHO2 RH H type (10K T3 thermistor) outdoor temperature and humidity sensor. We noticed that the wiring instructions are slightly incorrect; Terminal 4 needs a common connection. Please see the attached picture for reference.
Additionally, it’s difficult to understand the terminal numbers on the sensor, and the dip switches are so small that they are hard to see and switch, especially when standing on a ladder.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-23 07:13 AM
The diagram is correct, the voltage outputs should be referenced to pin 2 and not 4.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-23 07:13 AM
The diagram is correct, the voltage outputs should be referenced to pin 2 and not 4.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-24 01:13 AM . Last Modified: 2025-04-24 01:48 AM
I can confirm that the wiring diagram is not correct.
The diagram that's within the sensor's enclosure is correct, but the diagram on the paperwork is not
Pic of the diagram on the sensor. which is different to the paperwork
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-25 12:02 PM
Hello,
Can you confirm the full model number you are referring to. The SHO2 has models with temperature transmitter or passive RTD/ thermistor option. In the install there are two diagrams for wiring one for thermistor and one for transmitter. The one shown on the product refers to the RTD or Thermistor output.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-27 11:25 PM
As @Girish asked above, more information about the actual device.
A picture of the side of the sensor showing all product info will do.
Have you been in contact with the support about this issue?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-05 11:15 PM
Hey Girish,
The model in question is SHO2XA2H Outdoor humidity sensor, 2% RH, 10K T3 thermistor.
To clarify, the paperwork is incorrect. As shown in the picture below, the sensor diagram correctly indicates terminal 4 as Thermistor Out, whereas the paperwork incorrectly shows terminal 4 as open.
My installer couldn't work it out (via the paperwork), and the only answer I had was "it's not correct, use the diagram with the sensor"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-06 12:47 AM
@nigel_greenwave are you aware that the picture of the paper says Voltage mode, but the red arrow in the picture of t a device does come from the current connections?
Did they use Voltage or Current connections?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-06 10:41 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-07 12:12 AM
Can not say for sure for this model, but some of the sensors may have two different thermistors, there you select which one to use by the terminal to use.
One of the datasheet I found does say:
Temp. sensing element** 10K T3 thermistor, 1000 PT RTD
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-21 10:50 AM
@Girish please can you comment on the above
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-21 12:46 PM
Hello,
The install sheet should have two diagrams one for transmitter model like SHO2XA2A and other for thermistor or RTD model like SHO2XA2H/SHO2XA2C.
For SHO2XA2H please refer to the second diagram.