Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82514members
350118posts

ModbusTCP Citect

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

IngPianetti
Ensign
Ensign
0 Likes
7
1761

ModbusTCP Citect

Hi everybody!

 

I'm working with Citect 2016 (update 38).

 

We need to establish a Modbus TCP communication with a PLC in plant. Nevertheless, the SCADA never gets to communicate to this PLC. After running many tests, we found out that the SCADA never sends any kind of request to the mentioned PLC (we used wireshark). In order to rule out any kind network problem, we run a ModbusTCP Server in a PC which was at reach of the SCADA, but the results were the same. After that we proceed to create an empty new project pointing just to the same testing ModbusTCP Server. But to our surprise, it worked perfectly well, even though the parameters (port, protocol, device, variable addresses) were the same as the ones in our original project.

 

It is the first time something like this happend to us. We have many Schneider M340 using ModbusTCP without any kind of problems.

 

Any ideas?? Thanks in advance

 

7 Replies 7
AdamWoodland
Commander Commander
Commander
0 Likes
1
1735

Re: ModbusTCP Citect

Hi,

 

This section of the Community website is for the ClearSCADA / GeoSCADA product. For CitectSCADA / Plant SCADA product discussions try https://community.exchange.se.com/t5/Industry-Automation-and-Control/bd-p/industry-automation-contro...

 

Someone here might know, but you'll have more success at the Automation and Control section.

S_Stolyarov
Lieutenant JG
Lieutenant JG
0 Likes
3
1725

Re: ModbusTCP Citect

Am  I right that the new project in SCADA works well with Modbus TCP server?

IngPianetti
Ensign
Ensign
0 Likes
2
1719

Re: ModbusTCP Citect

Yes, you're totally right. 

 

The new project has only one device, which is the pc running the testing ModbusTCP server. With this simple configuration, the project is able to reach the test pc.

 

On the other hand, when the parameters of the pc are loaded to the original project, citect doesn't even send a modbus tcp frame to request data to this device, even when the parameters (device, port, protocol) are the same.

 

We're completely lost because we have many Schneider M340 running in plant with ModbusTCP without any issues.

IngPianetti
Ensign
Ensign
0 Likes
0
1718

ThabRe: ModbusTCP Citect

Thank you very much for your piece of advice. I'm new to this forum so, any help is well appreciated.

S_Stolyarov
Lieutenant JG
Lieutenant JG
0 Likes
1
1693

Re: ModbusTCP Citect

It is a very-very weird situation. Maybe you have somewhere doubled device with the same IP address in your original program?

kingslim
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1681

Re: ModbusTCP Citect

Tags (1)
IngPianetti
Ensign
Ensign
0 Likes
0
1664

Re: ModbusTCP Citect

Hi! 

 

It's a good guess. But it's not the case either. We run a a ModbusTCP client to simulate the SCADA on a computer to poll the remote device(PLC). The PLC always sent a response back. We did this first to make sure the PLC was working well but at the same time we checked the network

Tags (1)