Objective
The purpose of this article is to demonstrate the steps to configure the communication between the Modicon M262 dPAC controller and the Modicon M221 controller by using EtherNet/IP protocol.
Resolution
The attached document provides a step-by-step guide to configure the communication between the Modicon M262 dPAC controller and the Modicon M221 controller by using EtherNet/IP protocol.