Hello everybody.
Im using MPR-5610-704-0-4 with an eurotherm 3216 controller. i replace the actuator with the MPR-5610-0-0-4 and i realize the actuator is on all the time, but i put back the MPR-5610-704-0-4 actuator and is working fine. Both actuators looks like work from 4-20 mADC, but with MPR-5610-704-0-4 you can see the actuator moving back and forth, but with MPR-5610-0-0-4 eurotherm 3216 seens is not working. Both valves are working under the same controller
  • HVAC
Reply 1
ismailozinan
ismailozinan Leader
Leader
Posted: ‎2026-09-04 05:21 AM . Last Modified: ‎2026-09-04 05:21 AM
What is the MPR-5610-704-0-4?
  • Device: Proportional hydraulic actuator. It is not a schneider electric product.
  • Power Supply: 120V AC.
  • Control Signal: 4-20mA.
  • Feature: Spring return mechanism.
PLC Connection Instructions:
  • Wiring: Connect the actuator's signal input to either Analog Out 3 or Analog Out 4 on your PLC.
  • Configuration: Set the chosen output (AO 3 or AO 4) to 4-20mA mode in your PLC software.