Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

TM172PBG42RI: ERROR reading protection presence

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • TM172PBG42RI: ERROR reading protection presence
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
HuyDinh11
HuyDinh11
Explorer

Posted: ‎2026-06-05 01:18 AM . Last Modified: ‎2026-06-05 01:24 AM

0 Likes
8
611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-05 01:18 AM . Last Modified: ‎2026-06-05 01:24 AM

TM172PBG42RI: ERROR reading protection presence

I have some issue while using this TM172. When the program is clear, the program can download normally. But when I add some status variables, the download start to error like in the photo. What should I do to fix this?

HuyDinh11_0-1780647306281.png

also when I read all parameter in the commissioning tab the variable have this error

HuyDinh11_0-1780647837878.png

 

 

  • Tags:
  • english
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-06-24 11:49 PM

0 Likes
0
458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-24 11:49 PM

Hello,

I suggest to move to ESME HVAC 1.10, no reason to stay on an older version.

Production line is going to be updated to 596.17

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-06-16 11:41 PM

0 Likes
0
531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-16 11:41 PM

Hello,

 

if you can share a project with this error I can have a look at it

Reply

Link copied. Please paste this link to share this article on your social media post.

StevenCho
StevenCho
Contributor

Posted: ‎2026-06-22 01:36 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-22 01:36 AM

I am also facing same issue.

But I can't share the program file, because the customer don't share even with me.

 

I received requests for related verification from two different companies today alone.

Reply

Link copied. Please paste this link to share this article on your social media post.

StevenCho
StevenCho
Contributor

Posted: ‎2026-06-22 08:53 AM

0 Likes
0
499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-22 08:53 AM

I wanted to share a temporary workaround for a recent issue I encountered, in hopes it might help others facing a similar situation. Please note that this is based on my personal test results on-site, so I welcome any further insights from the experts here.

 

Observations:
There seems to be a potential compatibility issue between the built-in firmware version (596.13) of the recently shipped TM172 and previous software versions. Based on my findings, it appears to be a firmware-related behavior that might be resolved by upgrading to the latest software version (1.10.0).

 

The reasoning behind this assumption:

 

  1. No changes were made to the program file itself.

  2. The system worked properly when tested with the previous BIOS version (596.8).

  3. The same behavior occurred across two different units on-site.

 

Temporary Fix : 

Update the Software to 1.10.0, and upgrade both the Target and BIOS to 596.17.

 

*Note: If you enable 'Run-time check...' in the Project options, a system error WDT:111 may appear after the 'Download All' process is complete.wdt111.png

 

Troubleshooting Tip during BIOS Upgrade:
When downloading the BIOS on the target device (during 'DOWNLOAD ALL' or 'Write all' on commissioning), I initially couldn't proceed due to a System fault WDT:0 (likely caused by an interruption during the download).

 

To bypass this, I used the following steps:

  1. Downloaded a new, empty project to the device first.

  2. Then, proceeded with the BIOS upgrade.

 

Test Results for Reference


Issue Occurred:

  • ESME-HVAC 1.5.0 / 1.6.0 / 1.9.0 → Bios 596.13 / 596.16Error1.png

Resolved (No Error):

  • ESME-HVAC 1.6.0 → Bios 596.08

  • ESME-HVAC 1.10.0 → Bios 596.17

 

If anyone has a deeper understanding of this situation or a better solution, please help.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-06-23 09:04 AM

0 Likes
0
488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-23 09:04 AM

 

Hello,

I guess the reading protection presence Error is related to a feature added in MSK 596.14 and MSK 668.14.

The library sysProtectionFunction.pll available at C:\Program Files (x86)\Schneider Electric\EcoStruxureMachineExpertHVAC\Catalog\FreeAdvance\PLC allows to define a password to connect to TM172.

If you use a project target >= .14 and you connect to a firmware version <= .13, you might have this error.

Firmware version should be always >= project target version.

 

Run-time check... should be used only in simulation for debugging purposes, if they are used on a real target they might stop plc execution or a watchdog

 

At the end of a bios upgrade there is always a WDT:0, it is an expected watchdog, application will restart after 30sec during which all leds will be on.

Reply

Link copied. Please paste this link to share this article on your social media post.

StevenCho
StevenCho
Contributor

Posted: ‎2026-06-23 05:46 PM

0 Likes
0
482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-23 05:46 PM

Is it true that the problem I experienced and the problem he experienced are the same?

 

Based on my test, [ESME-HVAC 1.6.0 → Bios 596.08] was no problem.

[Project target < Firmware version]

 

Somehow, Issue on 596.13 was solved after update the latest firmware and target.

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

StevenCho
StevenCho
Contributor

Posted: ‎2026-06-24 01:43 AM

0 Likes
0
470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-24 01:43 AM

The same issue occurred at another client's site.

 

80 units of TM172PDG42RI were delivered to the site, and the problem occurred in 5 of them.

 

Commonly, a System Fault (WDT:0) occurred, just as it did previously (except for one unit, which experienced an infinite reboot).

Temporary fix were taken using the following method.

*Since BIOS updates cannot be performed while WDT:0 is active, the following steps are performed first.
BIos error.png

1. Create a new project (Empty Project File) and select Download PLC Code / Download ALL.

2. Download BIOS (From 596.13 to 596.13) - Same version.

3. Download existing program PLC Code → [Commissioning] Write All.

4. Download All.

 

The current conclusion is that the problem was resolved after Download the firmware of the same version.

 

By the way, the ESME-HVAC Version is 1.7.0 and Targer project & Firmware are 596.13.

Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-06-24 11:49 PM

0 Likes
0
459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-24 11:49 PM

Hello,

I suggest to move to ESME HVAC 1.10, no reason to stay on an older version.

Production line is going to be updated to 596.17

 

Reply

Link copied. Please paste this link to share this article on your social media post.

StevenCho
StevenCho
Contributor

Posted: ‎2026-06-25 07:05 AM . Last Modified: ‎2026-06-25 07:08 AM

0 Likes
0
452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-25 07:05 AM . Last Modified: ‎2026-06-25 07:08 AM

 

I recommend using the latest version, but it seems the update is being delayed because all team members (about 20) need to update for version compatibility.

 

By the way, is there any additional information available regarding these symptoms?

Additionally, it does not appear to be related to the production lot.

(Occurred in Week 15 of 2024 / Week 25 of 2025)

If this symptom occurs again, I will try to retrieve the product.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE