Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

TM172DCLWT

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • TM172DCLWT
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
otrotabi
otrotabi
Contributor

Posted: ‎2022-10-31 09:44 AM

0 Likes
5
2527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-31 09:44 AM

TM172DCLWT

We have only used this display once, long ago. I would like to confirm a few things:

 

1) They are meant to be programmed with HVAC ecostruxure machine expert

 

2) They are compatible with both TM171 and TM172 line (as long as hte PLC has Modbus)

 

3) This is only an opinion what I request, but we are being asked to place one of this inside a place which is quite dusty (actually it is powder milk in suspension). Besides the fact that the sensors might get blocked or become useless, is there anything else I should take care of ? Would a  regular HMI be a better solution ? They only need to take a look at a couple of variables.

Labels
  • Labels:
  • HVAC
  • Tags:
  • ecostruxure
  • english
  • hvac
  • TM171
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
LeTomas
LeTomas Mentor
Mentor

Posted: ‎2022-11-01 12:52 AM

0 Likes
4
2506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-01 12:52 AM

Hi @otrotabi 

 

The TM172D range of colour touch display is programmed using the EcoStruxure Machine Expert HVAC and is meant to communicate with the M172 controller or any other devices using Modbus Serial.

 

When we worked with the TM172DCLWT a few years ago , this was the only display available then we launch the TM172DCLFW and the TM172DCLFG that does not have any sensor embedded, so any of those can be a solution. Another cheaper (i guess) could be the TM172DGRP but you will need to check if this one is available in Argentina.

 

If you use an HMI programmed in Vijeo Designer (basic) or EcoStruxure Operator Terminal Expert i believe this solution could a little bit more expensive than using the display for the M172 offer but check it with your Schneider sales team.

 

Best regards,

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
LeTomas
LeTomas Mentor
Mentor

Posted: ‎2022-11-01 12:52 AM

0 Likes
4
2507
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-01 12:52 AM

Hi @otrotabi 

 

The TM172D range of colour touch display is programmed using the EcoStruxure Machine Expert HVAC and is meant to communicate with the M172 controller or any other devices using Modbus Serial.

 

When we worked with the TM172DCLWT a few years ago , this was the only display available then we launch the TM172DCLFW and the TM172DCLFG that does not have any sensor embedded, so any of those can be a solution. Another cheaper (i guess) could be the TM172DGRP but you will need to check if this one is available in Argentina.

 

If you use an HMI programmed in Vijeo Designer (basic) or EcoStruxure Operator Terminal Expert i believe this solution could a little bit more expensive than using the display for the M172 offer but check it with your Schneider sales team.

 

Best regards,

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
otrotabi
Contributor

Posted: ‎2022-11-01 04:05 AM

In response to LeTomas
0 Likes
3
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-01 04:05 AM

Thanks for your answer.

 

We are currently looking for an alternative to the TM171DLED which allowed us to have a flush interfase with the TM171 line. What we need is something we can mount on a chiller and is visible to an operator without the need to open a panel door.

 

Both the TM171DLED and the embedded display TM171OF22R are not available locally,  although as far as I know they are not officially discontinued  by SE internationally. 

 

I like TM172DCLWT but I have not figured out yet a good way to both mount and protect it for this particular use.

 

I just found that there is something called XBTN and XBTR small panels which can work with a Zelio relay for example. Have you ever used them ? Is it possible to connect them with a TM171 ?

 

xbnt.jpg

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

LeTomas
LeTomas Mentor
Mentor

Posted: ‎2022-11-01 05:16 AM

In response to otrotabi
0 Likes
0
2494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-01 05:16 AM

Hi @otrotabi ,

 

The family range XBTN is discontinued and we use the HMISTO7 range instead. This newer HMI is programmed in EcoStruxure Operator Terminal Expert and you will need a license for it , please check my next FAQ:

https://www.se.com/uk/en/faqs/FAQ000229667/

 

In your case, it will be good to have one software to program the solution like using the TM172DCLFG  which is similar as the TM172DCLWT but without the sensors and different mounting more close to an standard HMI.

 

Best regards,

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-11-02 01:01 AM

In response to otrotabi
0 Likes
1
2476
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-02 01:01 AM

Hi,

 

check if TM172DCLFG is available: 

https://www.se.com/ww/en/product/TM172DCLFG/modicon-m172-display-color-touchscreen-grey/

 

It is the flush mounting version of TM172DCLWT (without sensors and RTC).

 

Another flush mounting display is TM172DGRP, but it has to combined to a TM172 (connection is through CAN bus).

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
otrotabi
Contributor

Posted: ‎2022-11-02 04:31 AM

In response to FedericoM
0 Likes
0
2469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-02 04:31 AM

Thanks. Yes, I will consult with our salesman.

 

Regards

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore