Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

TM171OBM14R Cannot connect to target

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • TM171OBM14R Cannot connect to target
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
ORC_Orange53
ORC_Orange53
Explorer

Posted: ‎2026-08-12 01:59 AM

0 Likes
4
240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-12 01:59 AM

TM171OBM14R Cannot connect to target

Dear  Team,

I am experiencing a problem with the TM171OBM14R controller. The communication parameters as well as the BIOS parameters have been lost.

As a result, it is impossible to connect to the controller either via the ADMI interface or via Modbus RTU (several scans did not detect the device).

I have a screenshot of the BIOS parameters, but I do not trust it since it was taken by someone else a few days after the communication issue occurred.

Additionally, since this model does not have a display, I cannot access the BIOS directly.

Could you please advise whether it is possible to reset the device to factory settings, or if there is any chance to restore communication?

Thank you in advance for your assistance.

Best regards,

Attachments
Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2026-08-14 04:21 AM

0 Likes
0
210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-14 04:21 AM

And additional if it is modbus Master you have when i remember correct a few secounds during boot were you have the possibility to connect to the PLC via Modbus. And like Marco mentioned the easiest first way would via TM171DLED.

As alternative you could also try to set a new confiugration to the PLC via TM171AMFK

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
M_Cervati
M_Cervati Troubleshooter
Troubleshooter

Posted: ‎2026-08-13 06:02 AM . Last Modified: ‎2026-08-13 06:04 AM

0 Likes
0
235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-13 06:02 AM . Last Modified: ‎2026-08-13 06:04 AM

Hi,

do you know if TM171O is modbus master on port RS-485?

If yes, it is needed to disable the modbus master before to try to connect. Usually there is a parameter in a some menu, but in this case you need a TM171DLED to connect to the LAN.

If it is modbus slave, using ESME HVAC Installer it is possible to perform a scan on the port trying with different baud and different modbus address.

Check also the ADMI cable between PLC and ADMI,  a lot of plug-unplug could damage the cable. To test it connect to another PLC and connect.

Another solution is to check communication parameter using a remote display TM171DLED to LAN port of TM171O and verify the parameter CF30, CF31 and CF32.

 

Best regards

 

Marco Cervati

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2026-08-14 04:21 AM

0 Likes
0
211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-14 04:21 AM

And additional if it is modbus Master you have when i remember correct a few secounds during boot were you have the possibility to connect to the PLC via Modbus. And like Marco mentioned the easiest first way would via TM171DLED.

As alternative you could also try to set a new confiugration to the PLC via TM171AMFK

Reply

Link copied. Please paste this link to share this article on your social media post.

ORC_Orange53
ORC_Orange53
Explorer

Posted: ‎2026-08-16 12:31 AM

0 Likes
0
178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-16 12:31 AM

Dear Team,

Thank you very much for your advice.

I have tried different address options, but so far this has not led to any result. I also tested the ADMI adapter on another controller, and it works correctly.

I found a TM171DLCD2U and attempted to connect it to the LAN port to adjust the BIOS parameters, but the attempt was unsuccessful. After powering on, the display only shows dashes, and pressing the key combination does not allow me to enter the BIOS menu. At the same time, the TM171DLCD2U works normally with another controller.

My next step will be to attempt to select the correct Modbus connection parameters.

If there are any other options or checks you would recommend, I would greatly appreciate your advice.

Unfortunately, it is not possible for me to obtain a TM171DLED or TM171AMFK at this time.

Best regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-08-17 12:58 AM

0 Likes
0
175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-17 12:58 AM

Hello,

 

TM171DLCD2U shows only what has been defined in the project running on TM171O, TM171DLED is an echo of the local display and allows to access Bios menu.

 

The only solutions available are the one already suggested: 

- TM171DLED or

- TM171DLED + TM171AMFK

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore