Real Time Clock(RTC) M171O (Optimized) series controllers

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Real Time Clock(RTC) M171O (Optimized) series controllers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
76
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
52
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Solved
Josh1
Ensign Josh1
Ensign

Posted: ‎2021-05-26 02:35 AM

1 Like
2
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-26 02:35 AM

Real Time Clock(RTC) M171O (Optimized) series controllers

Hello,

Can anyone tell me, How to Access RTC Registers in modicon M171 Controller?

Thank You in Advance!

Labels
  • Labels:
  • Connectivity
  • HVAC
  • Modicon M2xx
  • Tags:
  • automation
  • english
  • ladder
  • plc
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-05-26 02:48 AM

0 Likes
1
1792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-26 02:48 AM

You can change the setting of the RTC through the display 

like TM171Oclock1.PNG

like shown in the online help or the user guide.

And you can use the follow target block (sysClockWrite)to set the RTC

TM171Oclock2.PNG

and you can read out the actual values from the struct Target Var sysclocl

TM171Oclock3.PNG

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 2
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-05-26 02:48 AM

0 Likes
1
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-26 02:48 AM

You can change the setting of the RTC through the display 

like TM171Oclock1.PNG

like shown in the online help or the user guide.

And you can use the follow target block (sysClockWrite)to set the RTC

TM171Oclock2.PNG

and you can read out the actual values from the struct Target Var sysclocl

TM171Oclock3.PNG

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Josh1
Ensign Josh1
Ensign

Posted: ‎2021-05-26 03:02 AM

In response to Bastian_Schmitz
0 Likes
0
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-26 03:02 AM

Thank You So much @Bastian_Schmitz  For Such a Quick and Great Response!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of