PWM output of TM173OFM22S connection to fan
HVAC and Pumping Forum
Select a Country
  • Industrial Automation
  • HVAC and Pumping Forum
  • PWM output of TM173OFM22S connection to fan
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
tlindenblatt
tlindenblatt
Explorer
Posted: ‎2026-07-06 09:15 AM
276
I want to control the PWM Input of a Papst 4154 N/2 H8P.
According to the manual the PWM-Input is open collector and expects a frequency of 2...10 kHz.
The fan has 4 wires:
24VDC
GND
PWM
Tacho
I've configured analog output 4 of my TM173OFM22S to provide a PWM frequency of 2kHz and variable duty cyle (set via the display).
Can I directly connect AO4 to the PWM input and Signal GND to GND or do I need to consider anything else? I could not find any further documentation about the open collector outputs.
The fan is powered by the same 24VDC/20A PSU as the TM173OFM22S.
Many thanks
Tobi
  • HVAC
FedericoM
FedericoM Mentor
Mentor
Posted: ‎2026-07-16 11:52 PM
you can connect AO4 configured as PWM to input and connect together the GND of Fan and TM173O.
M_Cervati
Troubleshooter
Posted: ‎2026-07-14 03:06 AM
240
Dear Tobi,
open collector PWM needs a pull-up resistor connected to 24VDC.
TM173O hasn't this resistor on board so verify if load to drive has this pull-up internally, otherwise you have to add externally, taking in account the maximum sink current is 50mA (like specified in hardware user guide).
Best regards
Marco Cervati
tlindenblatt
tlindenblatt
Explorer
Posted: ‎2026-07-15 01:09 AM
In response to M_Cervati
Dear Marco,
Thanks for the reply.
In the meantime I got a wiring diagram from the manufacturer:
The fan supply +UB is 24VDC
The internal reference is 5V and R1 is 10kOhm.
I'm a bit unsure because of this 5V internal reference. Can I connect AO4 to the PWM-Input, connect the grounds and everything works?
FedericoM
FedericoM Mentor
Mentor