Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PLC TM171 | Cannot connect to target

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Re: PLC TM171 | Cannot connect to target
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
Maiza
Maiza
Explorer

Posted: ‎2025-11-19 11:48 AM

0 Likes
3
709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-19 11:48 AM

PLC TM171 | Cannot connect to target

  • I've already tried using speeds of 9600 and 19200 with the E, 8, 1 and N, 8, 1 configurations. The same converter port configuration for these speeds has also been checked. I have 4 electrical panels out of service due to this problem and I'd like to find a solution without having to replace the PLC, as this is unacceptable. 

 

It looks like the communication board is burning out, it's very strange.

 

IMG-20251117-WA0016.jpg

 

Labels
  • Labels:
  • Connectivity
  • HVAC
  • Modicon M2xx
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2025-11-24 01:06 AM

0 Likes
0
652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-24 01:06 AM

Hello,

 

the RS485 port and TTL port of TM171O are the same serial, they can't be used at the same time.

Every time you change the serial settings of TM171O a reboot is needed.

 

You have only to configure the connection settings in order to be aligned to CF30,31,32.

If the controller is configured as modbus master, you can connect only at boot (modbus master will be disabled)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
M_Cervati
M_Cervati Troubleshooter
Troubleshooter

Posted: ‎2025-11-21 01:25 AM

0 Likes
1
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-21 01:25 AM

Hi, 

how is the connection mode? Using ADMI tool or port RS-485?

If you are using ADMI and you are using port on board RS-485 like master, you have to disable the master because the hardware port is the same.

If you are using ADMI or RS-4885 on board check the communication BIOS parameter CF30, CF31, CF32, using the BIOS menu navigation on keyboard and display.

If you are using LAN port in modbus check the communication BIOS parameter CF35, CF36, CF37,using the BIOS menu navigation on keyboard and display.

 

Best regards

 

Marco Cervati

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Maiza
Maiza
Explorer

Posted: ‎2025-11-22 06:15 AM

In response to M_Cervati
0 Likes
0
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-22 06:15 AM

Good morning, how are you? I managed to solve it yesterday, but I would like a technical explanation of how it works from you at Schneider (instinctively, it seems that EwDMI is based on the Modbus protocol, consequently, we have to transfer the programming according to this protocol). Well, the first few times we were only able to transfer the programming once, then we couldn't keep connecting the PLC to the computer and staying online. Since I needed to communicate with these PLCs on a single HMI, I set the Modbus configurations via the PLC display (CF30, CF31 and CF32), since we could no longer stay online through the programming. And yesterday, then, I went to Set Up Communication and configured the protocol (19200, Even, 8 and 1) in EwDMI and consequently its PLC address (Address), which I had set via the display and...it worked! I did the same test on 4 panels and that really is the solution. Now I would like a technical explanation at the EwDMI level, how it works and if this is indeed the procedure I just described.

Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2025-11-24 01:06 AM

0 Likes
0
653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-24 01:06 AM

Hello,

 

the RS485 port and TTL port of TM171O are the same serial, they can't be used at the same time.

Every time you change the serial settings of TM171O a reboot is needed.

 

You have only to configure the connection settings in order to be aligned to CF30,31,32.

If the controller is configured as modbus master, you can connect only at boot (modbus master will be disabled)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore