Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PAS600L M172

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Re: PAS600L M172
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
igor_climate_co
igor_climate_co
Contributor

Posted: ‎2024-07-23 11:51 PM

0 Likes
4
1479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-23 11:51 PM

PAS600L M172

Good day!

I can`t read Float32 from PAS600L - M172 does not display correctly variables. Display only ###### when M172 connected to serial line PAS600L. Without connected display 0.00.

Section Address (hexa) Register (dec) N° RW Unit Type Invalid Value Function Code Description
Current Metering Data 0x0BB7 3000 2 R A Float32 0xFFC00000 3, 100-4 RMS current on phase A

Other type registers reading correctly (RS485 thermostate for example). By using USB - RS485 converter reading Ok.

igor_climate_co_0-1721803524233.png

Who knows how to read registers PAS600L correctly? 

Many thanks.

Labels
  • Labels:
  • Connectivity
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
igor_climate_co
igor_climate_co
Contributor

Posted: ‎2024-11-11 06:59 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-11 06:59 AM

Thank you. The problem was solved. It is need to read 2 registers for current and 2 registers for voltage. Status variables must be: Installer type=Word, IEC type=Real. Then variables are interpreted via block Word2ToIEEE754.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2024-07-24 12:18 AM

0 Likes
1
1470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-24 12:18 AM

That the PASL also support Modbus RTU Server is new for me. But good to know.

If you get trouble on reading float values the problem could be the word order, the byte order  or the start address. Normally it should work. How do you read the values via TM172? Did you use configuration? You could try the modbus custom editor, this is in my opinion the easiest way in your case.

Reply

Link copied. Please paste this link to share this article on your social media post.

igor_climate_co
igor_climate_co
Contributor

Posted: ‎2024-07-25 05:07 AM

In response to Bastian_Schmitz
0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-25 05:07 AM

Thank you. 

About PASL server:

https://www.productinfo.schneider-electric.com/ecostruxurepanelserverguide/doca0172-ecostruxure-pane...

 

I tried a lot of combination modbus register types and +-addresses in ME but no result. Usialy used configuration. 

igor_climate_co_0-1721909041925.png

I`m looking  for mistake.

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2024-07-28 11:17 PM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-28 11:17 PM

Did you check sysMbmModbusRTUnodestatus target variable? Please check the response of the PAS. This could be helpfull to identifie the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

igor_climate_co
igor_climate_co
Contributor

Posted: ‎2024-11-11 06:59 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-11 06:59 AM

Thank you. The problem was solved. It is need to read 2 registers for current and 2 registers for voltage. Status variables must be: Installer type=Word, IEC type=Real. Then variables are interpreted via block Word2ToIEEE754.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore