Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-13 11:32 PM
Hi,
I'm looking at adding BBMD configuration settings to the HMI of a TM172PDG18R.
sysBACnet_BBMD does not provide too many details on how it works.
Do I have to continuously call 'sysBACnet_BBMD' as implied by 'BACnet Addons Lib User Guide v2.4'? Or is once sufficient per startup? Or once forever and then it sets EEPROM parameters in the background to start again?
Is calling it guaranteed to start the BBMD service? It returns 'TRUE' on every call, so it doesn't show if the service didn't start for any reason, such as if the provided inputs are invalid.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-20 11:13 PM
It can be called once, actually when it is called continously, it is really executed only when you change at least one function input (that's why we call it continously).
After a power cycle, you have to executed at least one time.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-19 12:09 AM
Hi,
it is called continously to allow to modify the settings runtime
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-20 06:39 PM
@FedericoM if I don't change the settings, does it need to be called continuously? Also, will the service start automatically after a power cycle if it was set prior to the power cycle?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-20 11:13 PM
It can be called once, actually when it is called continously, it is really executed only when you change at least one function input (that's why we call it continously).
After a power cycle, you have to executed at least one time.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.