M172 with Delta HMI type DOP107-EV

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • M172 with Delta HMI type DOP107-EV
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Captain FedericoM Captain
92
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
56
M_Cervati
M_Cervati Support
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
WADDAH
Crewman WADDAH
Crewman

Posted: ‎2025-11-02 04:05 AM

0 Likes
6
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-02 04:05 AM

M172 with Delta HMI type DOP107-EV

Dears .. The client has already bought a Delta HMI type DOP107-EV , and he want use it to read and write data from Modicon M172s that i have already programmed in his project . I configured the modicon M172s as slave , and the Delta DOP as a master .. I Have exported the modbus Data CSV File from M172s and tried to use addressed in the Delta DOP software but unfortunatelly I could not read data ... Are those addresses in CSV file can be used for all types of HMI .. Please help if you have any idea Best Regards #M172 #modicon #Machine
  • Tags:
  • @LeTomas
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Next Topic

Accepted Solutions
ismailozinan
Lt. Commander ismailozinan Lt. Commander
Lt. Commander

Posted: ‎2025-11-05 05:06 AM . Last Modified: ‎2025-11-05 05:54 AM

In response to WADDAH
1 Like
1
184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-05 05:06 AM . Last Modified: ‎2025-11-05 05:54 AM

Hi,

You can check via this link.

BR

 

11.jpg12.jpg

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
FedericoM
Captain FedericoM Captain
Captain

Posted: ‎2025-11-02 11:06 PM

0 Likes
0
264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-02 11:06 PM

Hello,

consider that all registers of TM172 are holding registers, you can use commands 3 for reading and 6,16 for writing. Registers are base 1, you can easily test using Modscan entering the same addresses.

Keep also in mind that TM172 answer with an exception if you try to read a not existing register with a multiple read (you might need to decrease the maximum number of registers to be read in one shot on Delta side).

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2025-11-03 05:28 AM

0 Likes
0
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-03 05:28 AM

And you get a big problem if you have not only continous register adresses.You have to check this point in ESME HVAC.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Lt. Commander ismailozinan Lt. Commander
Lt. Commander

Posted: ‎2025-11-03 06:22 AM

2 Likes
3
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-03 06:22 AM

Hi,

The variable ordering in the Delta panel's CSV file is different from that in the Schneider PLC's CSV file. It might be easier for you to first try a test by creating the variables individually in the Delta HMI, and then attempt to retrieve the data using the CSV file.

STEP-1STEP-1STEP-2STEP-2STEP-3STEP-3

Reply

Link copied. Please paste this link to share this article on your social media post.

WADDAH
Crewman WADDAH
Crewman

Posted: ‎2025-11-03 10:23 PM

In response to ismailozinan
0 Likes
2
227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-03 10:23 PM

 

Thanks

... I agree with you that we cann't use the exported csv data file from M172 Directly ... 

Could you please tell me how to put this address in Delta HMI DOP as an example ... 

HMI is the master and M172 is slave ...

Best Regards

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Lt. Commander ismailozinan Lt. Commander
Lt. Commander

Posted: ‎2025-11-05 05:06 AM . Last Modified: ‎2025-11-05 05:54 AM

In response to WADDAH
1 Like
1
185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-05 05:06 AM . Last Modified: ‎2025-11-05 05:54 AM

Hi,

You can check via this link.

BR

 

11.jpg12.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

WADDAH
Crewman WADDAH
Crewman

Posted: ‎2025-11-09 05:26 AM

In response to ismailozinan
0 Likes
0
90
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-09 05:26 AM

Thank you for you help full record... It was usefull. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore