Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

M172 PT1000 Analog Resistive Input

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • M172 PT1000 Analog Resistive Input
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
Hanif777
Hanif777
Explorer

Posted: ‎2023-04-06 11:03 PM

0 Likes
4
4389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-06 11:03 PM

M172 PT1000 Analog Resistive Input

Hello, I'm trying to integrate a  2-wire PT1000 into my M172

 

I've set the corresponding parameter ( in this case the Cfg_AI8 ) to 6=PT1000, and although I got some reading, I'm not quite sure what is it exactly (it hovers around 400 INT dropped to 160 when I put some ice)

 

So my question is:

1. Does the FullScaleMin_AI8 & FullScaleMax_AI8 parameters need to be adjusted too? I kept it default at 0...1000

2. Does the value gained from the local IO variable (AIL8) is still in Ohm or has it been converted to temperature?

3. If it's still in Ohm any quick conversion library / FB I can use instead of manual conversion?

 

That's all, thanks!!

Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2023-04-07 01:33 AM

0 Likes
1
4381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-07 01:33 AM

The sensor give a feedback with with one decimal place 100=10,0‘c 

fullscale min and max work only for current and voltage inputs. The gain is only used by n the factory to calibrate the inputs. 
please check if the Parameter for the unit is correct C/F .

and check if in your configuration the pair of AI is set to PT1000

 

best regards

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2023-04-07 01:33 AM

0 Likes
1
4382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-07 01:33 AM

The sensor give a feedback with with one decimal place 100=10,0‘c 

fullscale min and max work only for current and voltage inputs. The gain is only used by n the factory to calibrate the inputs. 
please check if the Parameter for the unit is correct C/F .

and check if in your configuration the pair of AI is set to PT1000

 

best regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Hanif777
Hanif777
Explorer

Posted: ‎2023-04-07 10:29 AM . Last Modified: ‎2023-04-07 10:29 AM

In response to Bastian_Schmitz
0 Likes
0
4366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-07 10:29 AM . Last Modified: ‎2023-04-07 10:29 AM

Alright I guess so, thanks!

 

That means I got 40.4 C ambient temp & 16.1 C when put with ice

 

Hmmm guess I need to recalibrate the sensor, or simply just not buy a cheap one 😕

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

kasmic_mike
kasmic_mike
Contributor

Posted: ‎2023-04-28 01:55 AM

0 Likes
1
4284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-28 01:55 AM

hi there, 

if you are using ESME for programming your plc i recommend you use the LIN_TRAFO function block to scale your sensor output. check out that link for detail

https://product-help.schneider-electric.com/Machine%20Expert/V2.0/zh/Util/Util/modules/LIN_TRAFO.htm...

KASMIC
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
otrotabi
Contributor

Posted: ‎2023-04-28 04:03 AM

In response to kasmic_mike
0 Likes
0
4280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-28 04:03 AM

Hi Mike,

 

What do you mean ? Are Codesys FB´s available as a library for ESME ? I asked some time ago and there´s no "official" implementation so far , at least the moment I asked there was not.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore