Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

M172 BACnet Communication with Other Controllers Example Needed

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • M172 BACnet Communication with Other Controllers Example Needed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Control Expert - HVAC Library

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
KrzysztofSoczewka
KrzysztofSoczewka
Contributor

Posted: ‎2026-04-02 05:09 AM

0 Likes
3
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-02 05:09 AM

M172 BACnet Communication with Other Controllers Example Needed

Hi,

I’m looking for a simple working example of BACnet communication from a Schneider Electric M172 (28–42 I/Os) to another BACnet device (any third-party controller), especially writing values (WriteProperty).

Does anyone have a sample project or configuration?

Thanks!

Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-04-08 07:36 AM

0 Likes
2
527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-08 07:36 AM

Hi,

this functionality will be available with ESME HVAC 1.10 which will be released in the coming weeks.

These functions will be available:

  • sysBACnet_RemRead() sends BACnet ReadProperty-A
  • sysBACnet_RemWrite() sends BACnet WriteProperty-A
  • sysBACnet_GetRequestStatus() monitors the status of the command sent to a server

Read and Write will be supported on the following objects and properties:

FedericoM_0-1775658949640.png

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

MargheritaM
MargheritaM Contributor
Contributor

Posted: ‎2026-06-10 12:20 AM

In response to KrzysztofSoczewka
0 Likes
0
310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-10 12:20 AM

Hi,

I am sharing with you an example project in which the TM172P operates as a BACnet client. In this example, it is possible to both read and write values from/to BACnet servers available on the network.

For implementing the read and write operations, we have used BACnetRemoteRead and BACnetRemoteWrite function blocks from the BACnet_Addons library, which is attached to this message in a beta version. These function blocks internally make use of the functions sysBACnet_RemRead(), sysBACnet_RemWrite(), and sysBACnet_GetRequestStatus(). By using the provided FBs, the interaction with these low-level functions is simplified, making the implementation more straightforward.

At the moment, this project should be considered as a starting example rather than a complete reference implementation.

If you have any feedback or additional requirements, we would be happy to review them and further improve the example accordingly.

Please let me know if you need additional clarification.
Margherita

See Answer In Context

Attachments
Demo project_260610.zip
BACnet_Addons_v2.5.0-BETA.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-04-08 07:36 AM

0 Likes
2
528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-08 07:36 AM

Hi,

this functionality will be available with ESME HVAC 1.10 which will be released in the coming weeks.

These functions will be available:

  • sysBACnet_RemRead() sends BACnet ReadProperty-A
  • sysBACnet_RemWrite() sends BACnet WriteProperty-A
  • sysBACnet_GetRequestStatus() monitors the status of the command sent to a server

Read and Write will be supported on the following objects and properties:

FedericoM_0-1775658949640.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

KrzysztofSoczewka
KrzysztofSoczewka
Contributor

Posted: ‎2026-06-09 12:44 AM

In response to FedericoM
0 Likes
1
329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-09 12:44 AM

Hi,

Thank you for the information.

Could you please provide a simple example of how to use sysBACnet_RemRead(), sysBACnet_RemWrite(), and sysBACnet_GetRequestStatus()?

I am particularly interested in a complete example showing:

  • Reading a BACnet Analog Value object from a remote device
  • Writing a value to a remote BACnet object
  • Monitoring the request status using sysBACnet_GetRequestStatus()
  • Typical parameter values and the recommended sequence of function calls

A small Machine Expert HVAC project example or code snippet would be greatly appreciated.

Thank you in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

MargheritaM
MargheritaM Contributor
Contributor

Posted: ‎2026-06-10 12:20 AM

In response to KrzysztofSoczewka
0 Likes
0
311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-10 12:20 AM

Hi,

I am sharing with you an example project in which the TM172P operates as a BACnet client. In this example, it is possible to both read and write values from/to BACnet servers available on the network.

For implementing the read and write operations, we have used BACnetRemoteRead and BACnetRemoteWrite function blocks from the BACnet_Addons library, which is attached to this message in a beta version. These function blocks internally make use of the functions sysBACnet_RemRead(), sysBACnet_RemWrite(), and sysBACnet_GetRequestStatus(). By using the provided FBs, the interaction with these low-level functions is simplified, making the implementation more straightforward.

At the moment, this project should be considered as a starting example rather than a complete reference implementation.

If you have any feedback or additional requirements, we would be happy to review them and further improve the example accordingly.

Please let me know if you need additional clarification.
Margherita

Attachments
Demo project_260610.zip
BACnet_Addons_v2.5.0-BETA.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.