Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to create typed enum?

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Re: How to create typed enum?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
obscuresc
obscuresc
Troubleshooter

Posted: ‎2022-04-13 10:53 PM

0 Likes
5
5369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-13 10:53 PM

How to create typed enum?

Hi,

 

It seems that enumerations default to a DINT type.

I would like to change the type to a USINT so I can avoid casting every use of the enum.

I also don't want the type to be DINT across the project because I don't need the range of a DINT and it just makes program heavier to run.

 

The enum is per the following

State: (
	Idle := 0,
	Pending := 2,
	Active := 3,
	Fault := 4
);

 

 

I've tried casting in the following manners;

 

State: (
	Idle := TO_USINT(0),
	Pending := TO_USINT(2),
	Active := TO_USINT(3),
	Fault := TO_USINT(4)
);


State: (
	Idle := 0,
	Pending := 2,
	Active := 3,
	Fault := 4
) USINT;

 

 

Thanks.

 

Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-04-13 11:12 PM

0 Likes
2
5362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-13 11:12 PM

Hi,

 

unfortunately there is not a way to specify the type of an Enumeration, which is assumed by the compiler as a DINT.

 

You should write:

 

usiVar := TO_USINT(State #Idle);

 

If you want to force a different type, I suggest to use CONSTANT variable, in this case you can specify the type.

If you want to define the type of an explicit value in your code, you can write USINT#5 and keep TO_USINT() for casting of variables, expressions.

 

Regards,

Federico 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-04-13 11:12 PM

0 Likes
2
5363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-13 11:12 PM

Hi,

 

unfortunately there is not a way to specify the type of an Enumeration, which is assumed by the compiler as a DINT.

 

You should write:

 

usiVar := TO_USINT(State #Idle);

 

If you want to force a different type, I suggest to use CONSTANT variable, in this case you can specify the type.

If you want to define the type of an explicit value in your code, you can write USINT#5 and keep TO_USINT() for casting of variables, expressions.

 

Regards,

Federico 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

obscuresc
obscuresc
Troubleshooter

Posted: ‎2022-04-13 11:26 PM

In response to FedericoM
0 Likes
1
5355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-13 11:26 PM

I was hoping to avoid having to cast each use of the enum.

Constant variables have lots of overhead because they have to be defined as VAR_EXTERNAL anyway.

 

DINT will have to suffice.

 

Thanks @FedericoM 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-04-13 11:38 PM

In response to obscuresc
1 Like
0
5349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-13 11:38 PM

Global constants can be used inside functions and fbs without the need of additional declaration inside the block

 

Federico 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

dFx
dFx
Explorer

Posted: ‎2022-04-20 11:39 PM

0 Likes
1
5242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-20 11:39 PM

As far as I know, with codesys you can : CODESYS Online Help

 

TYPE COLOR : ( white := 16#FFFFFF00, yellow := 16#FFFFFF00, green := 16#FF00FF00, blue := 16#FF0000FF, black := 16#88000000 ) DWORD := black; // Basic data type is DWORD, default initialization for all COLOR variables is black END_TYPE

 

Extensions to the IEC 61131-3 standard

The basic data type for an enumeration declaration is INT by default. However, you can also declare enumerations that are based explicitly on another integer data type.

basic data type : INT | UINT | SINT | USINT | DINT | UDINT | LINT | ULINT | BYTE | WORD | DWORD | LWORD

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-04-21 12:21 AM

In response to dFx
0 Likes
0
5234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-21 12:21 AM

Hello,

 

the question was related to the software Ecostruxure Machine Expert HVAC, which is not Codesys based.

 

Federico

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore