Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to communicate via the RS485/2 communication port on the Modicon M172 PLC?

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • How to communicate via the RS485/2 communication port on the Modicon M172 PLC?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
MaizaVitoriaCosta
MaizaVitoriaCosta
Explorer

Posted: ‎2026-02-10 11:36 AM . Last Modified: ‎2026-02-10 11:42 AM

0 Likes
7
3264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-10 11:36 AM . Last Modified: ‎2026-02-10 11:42 AM

How to communicate via the RS485/2 communication port on the Modicon M172 PLC?

 

I'm using a chiller with Modbus RTU communication. I tested direct communication between the chiller and a Modbus RS485 to USB converter. It worked perfectly using ModScan.

However, this chiller is not communicating with the RS485/2 port of my M172 PLC. I checked all the settings on the PLC and I don't see any configuration errors.

And on my RS485/1 port, I use an HMI (model HMIET6401). This data from the chiller will be received by the M172 PLC, which will consequently send this data to my HMI. Can anyone help me? I've tried everything.

Attachments
communication_direct_chiller.mp4
Labels
  • Labels:
  • Connectivity
  • HVAC
  • Modicon M2xx
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ismailozinan
ismailozinan Leader
Leader

Posted: ‎2026-02-13 11:55 PM

0 Likes
0
3171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-13 11:55 PM

Hi,

sample link is here 

I am sharing the folder where I placed the sample communication program link and the video link demonstrating Modbus communication using the TM221 PLC W50 (40051) and W51 (40052) addresses.

 

The M221 PLC operates as a slave device, similar to your chiller unit. You may proceed with your implementation by considering the M221 as the chiller and following this sample program.

 

I recommend downloading the program once using the Download All option. After confirming that your Modbus parameters are correct, please ensure that the USB cable is not connected to the PLC, then power cycle the PLC. Afterward, you may go online with the PLC.

I hope this will be helpful.

Best regards, and I wish you successful work.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-02-11 03:44 AM

0 Likes
1
3247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-11 03:44 AM

Hello,

some hints.

Check the value of:

FedericoM_1-1770810110457.png

Have you done a download all with reboot?

 

Check also the status of the following target variables:

FedericoM_2-1770810206568.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

MaizaVitoriaCosta
MaizaVitoriaCosta
Explorer

Posted: ‎2026-02-11 05:45 PM . Last Modified: ‎2026-02-11 05:48 PM

In response to FedericoM
0 Likes
0
3238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-11 05:45 PM . Last Modified: ‎2026-02-11 05:48 PM

Good evening. The "MbMRTU_DisByPar" item is enabled in the Miscellaneous tab. And yes, every time I send the program to the PLC, I restart it (unplug it from the power outlet and disconnect the USB cable).

 

miscellaneous_rs4852.png

 

 

 

 

Regarding the status items you mentioned, how would you perform a "MOVE" to identify those statuses? Do you have an example?

 

modbus_master.png

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-02-11 11:32 PM

0 Likes
1
3225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-11 11:32 PM

Drag & drop variables into the watch window, the index of the array is the node number you have specified on the slave when you have declared it in the Configuration section.

Reply

Link copied. Please paste this link to share this article on your social media post.

MaizaVitoriaCosta
MaizaVitoriaCosta
Explorer

Posted: ‎2026-02-12 04:22 AM

In response to FedericoM
0 Likes
0
3219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-12 04:22 AM

Good morning. I did it here. What does "FALSE" mean? See if it's correct, the images follow... the variables aren't matching.

WhatsApp Image 2026-02-12 at 09.08.13.jpegWhatsApp Image 2026-02-12 at 09.08.14 (1).jpegWhatsApp Image 2026-02-12 at 09.08.14.jpegWhatsApp Image 2026-02-12 at 09.08.15 (1).jpegWhatsApp Image 2026-02-12 at 09.08.15.jpeg

Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2026-02-12 11:57 PM

0 Likes
0
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-12 11:57 PM

I need to see the entire sysMbMrtuNodeStatus[11] in the watch window to better understand the situation.

If miss is false and pres is true, it works.

Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
ismailozinan Leader
Leader

Posted: ‎2026-02-13 11:55 PM

0 Likes
0
3172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-13 11:55 PM

Hi,

sample link is here 

I am sharing the folder where I placed the sample communication program link and the video link demonstrating Modbus communication using the TM221 PLC W50 (40051) and W51 (40052) addresses.

 

The M221 PLC operates as a slave device, similar to your chiller unit. You may proceed with your implementation by considering the M221 as the chiller and following this sample program.

 

I recommend downloading the program once using the Download All option. After confirming that your Modbus parameters are correct, please ensure that the USB cable is not connected to the PLC, then power cycle the PLC. Afterward, you may go online with the PLC.

I hope this will be helpful.

Best regards, and I wish you successful work.

Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
ismailozinan Leader
Leader

Posted: ‎2026-02-14 02:07 AM . Last Modified: ‎2026-02-14 02:12 AM

0 Likes
0
3160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-02-14 02:07 AM . Last Modified: ‎2026-02-14 02:12 AM

Hi,

is it possible try attached methods.

I am currently using the XBTZ9008 cable by cutting the RJ45 end and connecting only the Modbus A and B terminals to the TM172. This method works properly.

Although some people prefer to assemble the cable manually, I do not recommend this approach. There are specific pins inside the cable that need to be short-circuited. If this is not done correctly, it may cause issues, especially with non-isolated devices.

Thanks.

 

111.jpg1112.jpg

113.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore