Posted: 2021-06-07 09:42 PM
Hi,
I created a page to show fault history. In total, I have 10 Alarm alerts with a timestamp, which means 40 edit fields. But when I compile the program, I got an error:
=> Page Contains too many elements.
--- Start compilation (PreBuild) 1:57:33 PM ---
Generating IEC code for HMI...
ERROR generating IEC code for HMI
I removed them until I could compile them successfully. The total number of element I have on the screen is 32 edit fields. I haven't found any document where refers to maximum elements per page.
Does anyone know about this issue??
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-07 10:29 PM
To reduce the number of objects and to increase the number of possible alarm entry you can use a dynamic set list. In the attached PDF could you see how it works.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-09 04:22 PM
Thanks for your help. I could handle the navigation between pages and uses sets to manage the information displayed.
Link copied. Please paste this link to share this article on your social media post.