Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

EEPROM variable resetting after power loss

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Re: EEPROM variable resetting after power loss
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
otrotabi
otrotabi
Contributor

Posted: ‎2025-03-13 08:08 AM

0 Likes
2
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-13 08:08 AM

EEPROM variable resetting after power loss

I have just received a TM172PDG18S which has been working well so far for a couple of years.  I am asking this question before I connect it to my laptop, in case anyone has a suggestion before I do and eventually start changing anything.

 

The customer complained that the set-point went back to zero after a power loss so I powered it on, changed the set-point, powered off and after powering back on it turned out to be true, set-point went back to zero.

 

I changed a couple of other EEPROM variables and the new values were held after powering back on.

 

So my question is: is it possible that some memory positions in EEPROM can get damaged ? Or what else maybe the issue ?

 

 

 

 

Labels
  • Labels:
  • HVAC
  • Tags:
  • ecostruxure
  • english
  • hvac
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic

Accepted Solutions
M_Cervati
M_Cervati Troubleshooter
Troubleshooter

Posted: ‎2025-03-14 12:25 AM

0 Likes
1
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-14 12:25 AM

Hi,

eeprom location writing is performed by BIOS and there is a procedure to avoid unuseful writings, in fact if value to write is already the actual value it is not written. So I don't think the number of writings is over the maximum number of writings (worste case 100K). To write eeprom parametr are you using sysWritePadXXXX function block? If yes, are you checking the return value of this FB after execution?

Other possibility is from modbus channel. TM172 is master of a modbus network? If yes in the variables to write and read is there also the setpoint? If yes, the writing should be enabled after reading the parameter otherwise at start up setpoint not yet read is 0 and the modbus write overwrite the last value. So the best behaviour is disable writes at start up, read the modbus varaible, check if node is present and valid and then enable the modbus writes. 

 

Let me know.

 

Marco

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
M_Cervati
M_Cervati Troubleshooter
Troubleshooter

Posted: ‎2025-03-14 12:25 AM

0 Likes
1
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-14 12:25 AM

Hi,

eeprom location writing is performed by BIOS and there is a procedure to avoid unuseful writings, in fact if value to write is already the actual value it is not written. So I don't think the number of writings is over the maximum number of writings (worste case 100K). To write eeprom parametr are you using sysWritePadXXXX function block? If yes, are you checking the return value of this FB after execution?

Other possibility is from modbus channel. TM172 is master of a modbus network? If yes in the variables to write and read is there also the setpoint? If yes, the writing should be enabled after reading the parameter otherwise at start up setpoint not yet read is 0 and the modbus write overwrite the last value. So the best behaviour is disable writes at start up, read the modbus varaible, check if node is present and valid and then enable the modbus writes. 

 

Let me know.

 

Marco

Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
otrotabi
Contributor

Posted: ‎2025-03-14 05:25 AM

In response to M_Cervati
0 Likes
0
1152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-14 05:25 AM

Hi Marco and thanks for your support. 

 

Eeprom parameters are changed with the embedded display and not by a function block.

There´s no modbus communication but there´s a Can Bus communication. Maybe that is the issue. I am going to check and let you know.

 

Regards 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore