Posted: 2026-06-04 08:08 PM
i have a project that require a converter to read from VRV air conditioner BACnet MS/TP in a highrise building. and send the status of the VRV using BACnet IP.
can we used M172 to solve this?
David Chen
Tri Mitra Otomasi
IAD Certified (Indonesia)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-06-09 12:28 AM
Hello,
fw .17 includes some BACnet client functionalities which allows to read/write object properties:
But BACnet IP and MS/TP can be active at the same time.
You will need 2 TM172:
TM172 A: BACnet/IP + Modbus client of TM172 B (Tcp or rtu)
TM172 B: BACnet MS/TP + Modbus server of TM172 A (Tcp or rtu)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-06-09 12:28 AM
Hello,
fw .17 includes some BACnet client functionalities which allows to read/write object properties:
But BACnet IP and MS/TP can be active at the same time.
You will need 2 TM172:
TM172 A: BACnet/IP + Modbus client of TM172 B (Tcp or rtu)
TM172 B: BACnet MS/TP + Modbus server of TM172 A (Tcp or rtu)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-06-09 03:31 AM
hi, do you mean i have to DOWNGRADE my M172 firmware to 17?
can you share the firmware file here? or email to my email:
david.chen@trimitraotomasi.com
engineer@trimitraotomasi.com
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-06-09 11:31 PM
Hi,
it is not a downgrade, the latest fw for TM172 28/42 IOs is 596.17, the latest for TM172 7/18 IOs is 668.17.
They come with Ecostruxure Machine Expert HVAC 1.10 available on SE website
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-06-10 04:00 AM
Hello,
what are the changes for client mode?? is an additional communication module needed??
because I read in the ecostruxure machine expert - HVAC- Operating Guide, the protocol supported is bacnet MSTP (Server) and bacnet IP (Server)
Link copied. Please paste this link to share this article on your social media post.