3 phase pump connected to single phase power source
HVAC and Pumping Forum
Select a Country
  • Industrial Automation
  • HVAC and Pumping Forum
  • 3 phase pump connected to single phase power source
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
Moath
Moath
Explorer
Posted: ‎2026-03-16 01:30 AM
546
We have a pump rated at 0.55 kW, 3-phase, 380 V, which we would like to operate using a single-phase 220V power source.
Is there a recommended solution to start and operate the pump under this configuration
Bastian_Schmitz
Champion
Posted: ‎2026-03-19 11:07 PM
530
If the pump has the possibility to connect via star (400v) and delta (230V) you could connect the pump in delta wiring to a one phase VSD like ATV12 or ATV320 or ATH230. This configuration will be work. Then you need to use the motor name plate values for delta connection.
Bastian_Schmitz
Champion
531
Moath
Moath
Explorer
Posted: ‎2026-03-29 11:00 PM
In response to Bastian_Schmitz
Thank you for your reply, the pump is 400V on delta. is there any other recommended solution?