Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

SCADAPack x70 Integration with RemoteConnect

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • SCADAPack x70 Integration with RemoteConnect
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • Lists, Events & Alarms 21
  • WebX 19
  • Request Form 18
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 7
  • Mimic Graphics 7
  • Downloads 6
  • Support 5
  • IoT 5
  • Drivers and Communications 4
  • security 4
  • SCADA 4
  • Geo SCADA Expert 4
  • DNP 3 3
  • IEC 61131-3 Logic 3
  • Events & Alarms 2
  • Trends and Historian 2
  • Virtual ViewX 2
  • Lists 2
  • Privacy Policy 1
  • OPC-UA 1
  • Architectures 1
  • Templates and Instances 1
  • ClearSCADA 1
  • Releases 1
  • Maps and GIS 1
  • Tools & Resources 1
  • Mobile 1
  • Geo Scada 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Geo SCADA Expert 2022
  • Geo SCADA 2022 Operating System Support
  • Geo SCADA 2022 Upgrade Strategy
  • Geo SCADA 2022 Upgrade Notes
  • Geo SCADA 2022 Known Issues
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
sbeadle1
Spock sbeadle1 Spock
Spock
‎2021-06-09 02:52 PM
0 Likes
0
1897
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 02:52 PM

SCADAPack x70 Integration with RemoteConnect

Originally published on Geo SCADA Knowledge Base by sbeadle1 | June 09, 2021 11:52 PM

📖 Home  Back  

 

This guide takes you through the integration of SCADAPack x70 configuration within Geo SCADA Expert and the RemoteConnect software.

 

It's an overview of the integration capability with some tips. Please see the product help for a full description.


This support is available from ClearSCADA 2017 R3 and RemoteConnect R2.3.1. New facilities have been added to successive releases, and in particular the release of Geo SCADA 2021 brought configuration upload AND download capability!

 

These features are described first.

 

For those using Geo SCADA 2020 and earlier, please read the section after this one titled: "Geo SCADA and SCADAPack x70 Configuration Lifecycle up to Geo SCADA 2020".

 

Geo SCADA Expert and SCADAPack x70 Configuration Lifecycle from Geo SCADA Expert 2021

Compatibility

Geo SCADA Expert is 2021 - this release supports features for SCADAPack x70 from release 2.0 to release 2.6.1 (Firmware 9.6.1). These are supported by RemoteConnect versions 3.4.1 to 3.9.1.

 

Features in SCADAPack x70 2.7.3 (Firmware 9.7.3) are supported in Geo SCADA 2022. If your projects do not use these features then all other features are compatible:

  • Data logging - this is primarily a feature for RemoteConnect so it can display trends. The data that is logged is already reported to Geo SCADA Expert through ordinary DNP3 events.
  • Support for Modbus broadcast (for Modbus RTU server).
  • Support for structured IEC 60870-5-104 information object addresses (IOA).

Geo SCADA does not yet support managing the configuration (import/export/download/upload) of these three new features. If you were to import/upload a configuration to Geo SCADA Expert 2021 that uses these new features then the settings will be lost and a warning generated (in the configuration report) to inform you what was lost.

 

Overview

Geo SCADA Expert 2021 and upwards support the upload of configuration from SCADAPack 470 and 570 RTU types. For the first time, Geo SCADA Expert and SCADAPack join forces to support both upload and download of device configuration. Users can make changes locally using Remote Connect, or remotely using Geo SCADA Expert, allowing configuration to be managed and synchronized according to a customer’s working practices. The configuration forms for x70 devices in Geo SCADA Expert mirror the operations of the Remote Connect tool, and changes can be imported and exported from Geo SCADA Expert.

 

A site technician can set up an RTU, then use Geo SCADA to upload configuration. This makes hardware replacement simpler – just set up the initial communications channel, connect to Geo SCADA and send configuration down. If someone makes changes to the alarm settings on a site, a retrieval of configuration will ensure it’s not lost.

 

Screenshot 2022-08-04 121220.jpg

 

Configuration Lifecycle

Please click this link to work through the configuration lifecycle by example.

 

Geo SCADA Expert and SCADAPack x70 Configuration Lifecycle up to Geo SCADA Expert 2020

This section is relevant if you are using Geo SCADA 2020 and earlier.

System Diagram
GS-RC Integ 1.PNGGS-RC Integ 1.PNG

  • From ClearSCADA 2017 R3 a rich centralized configuration management environment for SCADAPack 57x devices is provided, using the advanced SCADAPack x70 driver. It Supports SCADAPack 570, 574 and 575 device models.

 

  • It uses DNP3 communications between Geo SCADA and SCADAPack 57x devices



Features and platforms to be included in a future version of the Geo SCADA SCADAPack x70 driver include:

  • Importing configuration changes from RemoteConnect and field devices into Geo SCADA objects

 

  • SCADAPack 470, 474 device models

 

  • Configuration of Object Browser tables that can be used by RemoteConnect



Recommendations (see diagram):

  • IT Network - Install Geo SCADA ViewX and SCADAPack RemoteConnect software on an Engineering Workstation for managing integration of configuration 

 

  • Follow Workflow steps 1-11 below for using ViewX and RemoteConnect together in managing SCADAPack 57x device configuration

 

  • Remote OT Network or local connection to SCADAPack device - Use RemoteConnect on a separate laptop or PC for field or remote connection to a SCADAPack 57x device

 

  • Follow Workflow steps 12-16 for maintenance and where unexpected configuration changes are made in the field, or remotely



Workflow



See diagrams below.

1. Create Geo SCADA SCADAPack x70 device & Configuration Objects

  • Create SCADAPack x70 Point Configuration Objects required for Logic variables (with appropriate T_SPx70_ Logic Types and Task settings)

 

  • Create SCADAPack x70 Point Configuration Objects and Point Protocol Objects for remote data communication with Geo SCADA

 

  • Create SCADAPack x70 Point Configuration Objects required for other local objects in the SCADAPack x70 (e.g. for DNP3 Peer communication, I/O, Modbus communication status objects, etc.)



2. On the Geo SCADA SCADAPack 57x Device object, use the Export to RemoteConnect method 

  • Export an RTZ file


Start the RemoteConnect application & create a project

3. In the RemoteConnect offline Logic page use the Advanced section Import button

4. Import RTZ file from Geo SCADA (as created in step 2), then save the RemoteConnect project.

5. Create or modify logic & objects using RemoteConnect and the SCADAPack x70 Logic Editor

  • Any new objects added to RemoteConnect for use in logic must also be added to Geo SCADA in Step 9

 

  • Changes to the T_SPx70_ Logic Type attribute or the Logic Task attribute of RemoteConnect objects must have their corresponding attributes updated in Geo SCADA in Step 9

 

  • Other object attribute and configuration changes made in RemoteConnect are not updated in Geo SCADA upon an Import. Make configuration changes in Geo SCADA objects only

 

  • Perform a 'Save As" in RemoteConnect to select which directory they would like the project saved in and to initially save it



6. Using the buttons on the RemoteConnect offline Logic page, select Open Editor and use the Update & Build Logic button to generate a complete RTU configuration / logic project

  • RemoteConnect generates an RTZ file in the project folder, based on the logic editor's Project Name property (default: Project.RTZ)



7. Save the RemoteConnect project

8. Use the Import From RemoteConnect method on the Geo SCADA SCADAPack 57x Device object

  • Select the RTZ file located in the RemoteConnect project folder (from step 6)

 

  • Geo SCADA validates RemoteConnect objects & imports the logic application



9. Create or modify Geo SCADA configuration objects for Logic, as needed

  • Correct any configuration highlighted by Geo SCADA validation in step 8



10. Repeat steps 2-9 or just step 2 as needed to complete logic and associated object settings

11. When Geo SCADA communication with the SCADAPack x70 RTU is operational,

  • use the SCADAPack x70 DNP3 Direct Outstation Download Configuration method to write the configuration to the remote RTU



  • Where possible, configuration changes for the SCADAPack 57x device should be performed using Geo SCADA and RemoteConnect as described in steps 2-9



  • Other on-demand changes required in the SCADAPack 57x device in the field (or remotely) by RemoteConnect should follow these steps:




GS-RC Integ 2.PNGGS-RC Integ 2.PNG


12. Connect laptop or PC to SCADAPack RTU and start RemoteConnect


13. Read Project from SCADAPack RTU


14. Modify configuration or logic as required, following steps as described in 5,6 and 7

15. Write Configuration to Device

  •  Take care that manual configuration or logic changes made to a SCADAPack 57x in the field (or remotely) by RemoteConnect may be overwritten by Geo SCADA (as it is the centralized configuration manager). There will not be a notification sent to Geo SCADA when these manual changes occur.



16. Obtain the RTZ file from RemoteConnect project folder on the laptop or PC that made the changes in the field, or remotely

  •  Manual changes that you wish to be made permanent in the Geo SCADA configuration should be applied using steps 8-11 as soon as possible



GS-RC Integ 3.PNGGS-RC Integ 3.PNG

Go: Home Back

Author

Biography

sbeadle1

Link copied. Please paste this link to share this article on your social media post.

  • Back to Stream
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc