Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Microsoft Update Testing - Archive

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Microsoft Update Testing - Archive
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Mimic Graphics 7
  • Events & Alarms 7
  • Lists 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Security 5
  • Drivers and Communications 4
  • IEC 61131-3 Logic 3
  • 2025 3
  • DNP 3 3
  • Geo Scada 2
  • Trends and Historian 2
  • Python 2
  • Virtual ViewX 2
  • Archive 1
  • Architectures 1
  • PI 1
  • Python API 1
  • Driver Kit 1
  • Code 1
  • Historian 1
  • Updates 1
  • OPC-UA 1
  • Privacy Policy 1
  • ClearSCADA 1
  • Mobile 1
  • Maps and GIS 1
  • Releases 1
  • Templates and Instances 1
  • AVEVA 1
  • Tools & Resources 1
  • Web 1
  • Previous
  • 1 of 5
  • Next
Latest Blog Posts
  • Microsoft Update Testing - Archive
  • PI Integration
  • Python API - Q and A
  • Python API - Create a custom web site serving Geo SCADA data using Flask
  • Configuration Examples
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
sbeadle
sbeadle Champion
Champion
‎2026-03-02 06:32 AM
0 Likes
0
319
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-02 06:32 AM

Microsoft Update Testing - Archive

Originally published on Geo SCADA Knowledge Base by sbeadle | March 02, 2026 03:32 PM

📖 Home  

Archived items from Microsoft Update Testing

Items prior to 2024.

 

Incompatibility Warning

Added 15 Dec 2023, Updated 16 Dec 2023, Updated 18 Dec 2023, Updated 21 Dec 2023.
Operating Systems Any using Windows Defender
Geo SCADA Versions

Geo SCADA releases made from December 2022 to September 2023 inclusive, including versions of 2019, 2020, 2021 and 2022. 

Parts of Geo SCADA Affected Microsoft Windows Defender quarantines various Geo SCADA client and server executable programs and DLLs
Specific Patches

Windows Defender Security intelligence update version 1.403.485 and higher. Released on Dec/15/2023 2:43:15 PM.

 

See https://www.microsoft.com/en-us/wdsi/definitions/antimalware-definition-release-notes?requestVersion... 

 

Up to but not including:

 

Windows Defender Security intelligence update version 1.403.810 and higher. Released on Dec/21/2023.

 

Several prior versions (up to four days before) do not exhibit the issue.

 

While Microsoft have received our software for their checks, we may not get a 'final' confirmation from them that they resolved the false positive. 

Symptoms Loss of Geo SCADA server and client functionality. 
Mitigation

Microsoft have been informed of this issue.

 

Requirement to add exclusions for Geo SCADA files and to reinstall Geo SCADA.

Resolved by

Resolved. Use Windows Defender definitions 1.403.870 (21 Dec 2023) onwards.

Refer to this for advice:

Geo SCADA KB Anti-malware-Configuration 

 

Incompatibility Warning

Added 30 Jan 2023
Operating Systems Windows Server 2022, 2019, 2016 and 2012 R2. Windows 11 and Windows 10.
Geo SCADA Versions Geo SCADA 2022 Initial Release
Parts of Geo SCADA Affected Installation of OPC UA Server Prerequisites
Specific Patches Windows Server 2022: KB5020877 – December 13, 2022 Cumulative Update for .NET Framework 3.5 and 4.8 (no January 2023 version available)
Windows Server 2019: KB5020874 – December 13, 2022 Cumulative Update for .NET Framework 3.5 and 4.8 (no January 2023 version available)
Windows Server 2016: KB5020873 – December 13, 2022 Cumulative Update for .NET Framework 4.8 (no January 2023 version available)
Windows Server 2012 R2: KB5020878 – December 13, 2022 Security and Quality Rollup for .NET Framework 4.8 (no January 2023 version available)
Windows 11: KB5020875 – December 13, 2022 Cumulative Update for .NET Framework 3.5 and 4.8
Windows 11: KB5022407 – January 19, 2023 Cumulative Update for .NET Framework 3.5, and 4.8
Windows 10: KB5020872 – December 13, 2022 Cumulative Update for .NET Framework 3.5 and 4.8
Windows 10: KB5022405 – January 19, 2023 Cumulative Update Preview for .NET Framework 3.5 and 4.8
Symptoms Failure to install the Aveva PCS Prerequisites for OPC UA Server. There is no problem if these Prerequisites are not chosen.
Mitigation Microsoft have recognised that their update has caused a problem. They have provided a workaround in the following link: https://support.microsoft.com/en-gb/topic/kb5022083-change-in-how-wpf-based-applications-render-xps-... We confirm that the Microsoft workaround resolves the issue until a future Microsoft update removes the need to use it.

Without the workaround, if the OPC UA Server is required please install Geo SCADA 2022 before installing the above Windows updates (or future patch rollups containing this same update). AVEVA is also working to resolve this in the installer, which may be included in a Monthly Update to Geo SCADA 2022.

Please check back here for updates.

Resolved by Microsoft Updates for .Net Framework for February 2023

 

Incompatibility Warning

Added 3 Nov 2022, Updated 6 Jan 2023 and 30 Jan 2023
Operating Systems Windows 10, 11, Server 2012 R2, Server 2016, Server 2019 and Server 2022
Geo SCADA Versions Geo SCADA 2021
Parts of Geo SCADA Affected ViewX Client
Specific Patches 2022-10 Cumulative Update for .NET Framework 3.5, 4.8 and 4.8.1 for Windows 10 Version 21H2 (KB5018545)
2022-10 Cumulative Update for .NET Framework 3.5, 4.8 and 4.8.1 for Windows 10 Version 21H1 (KB5018544)
2022-10 Cumulative Update for .NET Framework 3.5, 4.8 and 4.8.1 for Windows 11 (KB5018546)
2022-10 Security and Quality Rollup for .NET Framework 3.5, 4.6.2, 4.7, 4.7.1, 4.7.2, 4.8 for Windows 8.1, RT 8.1, and Windows Server 2012 R2 (KB5018549)
2022-10 Cumulative Update for .NET Framework 4.8 for Windows 10, version 1607 and Windows Server 2016 (KB5018515)
2022-10 Cumulative Update for .NET Framework 3.5, 4.7.2 and 4.8 for Windows 10, version 1809 and Windows Server 2019 (KB5018542)
2022-10 Cumulative Update for .NET Framework 3.5, 4.8 and 4.8.1 for Microsoft server operating system version 21H2 (KB5018551)
Symptoms If the user uses the 'Locate in Database' option from a list and then logs out of ViewX, ViewX will crash and a minidump will be generated. The Windows Update changes are known to affect applications using the Actipro tree list control, used by the ViewX database tree.
Mitigation a) Do not install this update (or future patch rollups containing this same update) until either:
  i) You have installed the Microsoft December 2022 rollup updates.
  ii) You have installed the Geo SCADA update issued in December 2022.
b) There is a workaround from Microsoft.
Add this line to the file SE.SCADA.ViewX.exe.config file in Program Files (x86). (Place the line before the existing text </runtime>):
  <AppContextSwitchOverrides value= "Switch.System.Windows.Controls.VirtualizingStackPanel.OptOutOfCollectionChangeFix=true"/>
  </runtime>
Resolved by Microsoft Updates for .Net Framework for February 2023

 

Incompatibility Warning

Added 27 June 2022, Updated 6 Jan 2023
Operating Systems Windows Server 2019
Geo SCADA Versions Geo SCADA 2019, 2020 and 2021, except 2022 and 2021 from December 2022
Parts of Geo SCADA Affected Virtual ViewX Server
Specific Patches 2022-06 Cumulative Update for Windows Server 2019 for x64-based Systems (KB5014692)
Symptoms Only one user will be permitted to log in to Virtual ViewX
Mitigation

Do not install this update (or future patch rollups containing this same update) until you have installed the December 2022 update of Geo SCADA 2021, or Geo SCADA 2022.

Resolved by December 2022 update of Geo SCADA 2021, or Geo SCADA 2022

 

Please note - A potential issue with Geo SCADA WebX ActiveX and Windows Updates KB5033371 and
KB5033372. The symptom is that scroll bars in ActiveX WebX do not function. This was resolved by Microsoft in their updates the following month.

 

 

Labels:
  • Archive

  • Security

  • Updates

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA

Author

Biography

sbeadle

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore