Hi,
what's the fastest and easiest way to import a PAS600 into PME?
Thank you and best regards
Link copied. Please paste this link to share this article on your social media post.
Hello @leomauro ,
The device type for PowerTag Rope in PME is " PowerTag Rope a F160".
If your devices are integrated in EBO I strongly recommend to use the EcoStruxure Web Services to make EBO communicates data with PME database.
All instruction here:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @leomauro,
What are the devices connected to your PAS600 ?
Fastest way is to declare the connected device in PME Management Console and let PME manage data logging.
If you want to publish your data (CSV) and transfer to PME, you need to use the ETL tool for PME:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @Romain_Polette ,
Thanks for your reply.
What I want to do is integrate the PAS600 into the PME, but I haven't figured out where or how to add it: I connected a PowerTag Rope 600A 3P/3P+N (A9MEM1591) to the PAS600, and I can see the data correctly in EBO via Modbus TCP/IP, but I don't know what type of device to use in the PME.
I searched for some information online, but I didn't find what I needed.
Thank you and best regards
Mauro
Link copied. Please paste this link to share this article on your social media post.
Hello @leomauro ,
The device type for PowerTag Rope in PME is " PowerTag Rope a F160".
If your devices are integrated in EBO I strongly recommend to use the EcoStruxure Web Services to make EBO communicates data with PME database.
All instruction here:
Regards,