Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

EGX300 support of Masterpact over IFM/IFE

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Re: EGX300 support of Masterpact over IFM/IFE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
104
Guillaume_Evrard
Commander Guillaume_Evrard Commander
46
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
31
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
dborle
dborle Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-02-23 01:21 AM

2 Likes
16
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-23 01:21 AM

EGX300 support of Masterpact over IFM/IFE

Hi,

Are there some plans to integrate a device driver into the EGX300 for supporting the new Micrologic trip units for Masterpact that are connected over IFM/IFE? We have more and more installations with this configuration with sometimes already existing EGX300. For sure one can develop a device driver, but unfortunately there is the disadvantage that you can't see the status of the trip unit in this case and the format of the real time pages is different to the one of the standard devices.

Thanks

Daniel

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-04-02 06:23 AM

0 Likes
0
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-02 06:23 AM

Hi Daniel/Magnus,

Sorry I missed this question.

As you may know, the EGX300 will be substituted by the Com'X 510 throughout this year.  We do not have on the roadmap to add more functionality into the EGX300 at this time.  Let me see if we can provide any other suggestions.

See Answer In Context

Reply
Replies 16
MagnusEngstrom
Ensign MagnusEngstrom Ensign
Ensign

Posted: ‎2015-04-02 12:37 AM

0 Likes
14
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-02 12:37 AM

Hello Daniel,

We have the same issue in Sweden. We are seeing some major customer dissatisfaction when they realize that our latest COM-solution for Masterpact doesn't work with the EGX300 w. latest F/W ... They expect a plug-and-play functionality, as usual!

Priority number one would be to have Masterpact with IFM + IO module for chassis management integrated in EGX300 web pages.

Regards // Magnus

Reply
dborle
dborle Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-04-02 12:53 AM

0 Likes
1
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-02 12:53 AM

Hi Magnus,

Good to hear that also someone else has the same problem than us!

Unfortunately there is no answer on this question until today.

I totally agree with you. The only solution that I found is either to use the NSX driver instead of Masterpact, but then the energy values are wrong (this is the only difference between the "new" Masterpact and NSX) or then you can write a custom driver, but this one can't show the breaker status. So both are not ideal solutions.

please can you give us an answer on this request?

Thanks

Daniel

Reply
sesa77557
sesa77557 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-04-02 12:54 AM

0 Likes
11
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-02 12:54 AM

- Paolo/Patrizio what do you think about?

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-04-02 06:23 AM

0 Likes
0
3448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-02 06:23 AM

Hi Daniel/Magnus,

Sorry I missed this question.

As you may know, the EGX300 will be substituted by the Com'X 510 throughout this year.  We do not have on the roadmap to add more functionality into the EGX300 at this time.  Let me see if we can provide any other suggestions.

Reply
paolobuonsanti
paolobuonsanti Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-04-08 03:05 AM

0 Likes
10
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-08 03:05 AM

I undestand that Com'X510 will replace the EGX300 range end of this year but we launched Enerlin'X IFE last year and we have to wait one year for having a real plug and play solution...I believe that we are not giving the right message to the market.

In addition we have the same problem on Com'X200 where the integration with a Masterpact/Compact with IFE have to be done with a custom device generator!!!

So in my opinion it's not a problem only linked to EGX300 but in general about the integration of Enerlin'X range inside the Com'X/EGX solution.

It's a real pity not to make the most of our complete portfolio to push the smart panel concept.

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-04-08 06:49 AM

0 Likes
9
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-08 06:49 AM

Ciao Paolo.

Just a note..the Com'X 510 will substitute the EGX300 beginning this month in Countries where launched.  The Com'X 200 also does support the IFE and Masterpact/Compact natively today.  Can you explain the need a custom device for this?

One last note...We do plan to have one last EGX300 update, but keeping the update to a minimal (minor bug fixes).  I have requested estimates from engineering to include the addition of IFE support...but there is no guarantee at this time.  I will have more to share on this next week.

Reply
paolobuonsanti
paolobuonsanti Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-04-08 07:40 AM

0 Likes
0
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-08 07:40 AM

Ciao James,

looking at this post it seems that Masterpact and Compact with IFE are not native inside the Com'X200/210..

https://powersolutionscommunity.schneider-electric.com/docs/DOC-3542?et=watches.email.document_comme...

Reply
MagnusEngstrom
Ensign MagnusEngstrom Ensign
Ensign

Posted: ‎2015-04-21 07:29 AM

1 Like
7
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-21 07:29 AM

Hi James,

In my mind, we have a greater need for EGX300 support of Masterpact/Compact NS with IFM (Modbus RS485) and IO module for chassis management. The IFE is already on Ethernet/Modbus TCP and has web pages of its own.

We have a large installed base of EGX300's all over the world, and it is clear that many of these installations will be upgraded or expanded in the near future. The least we should do is ensure that it supports all the devices commercialized up until its own end of commercialization ...

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-04-21 10:35 AM

0 Likes
6
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-21 10:35 AM

Understood.  Just an update for everyone.

I met with the engineering team last week, and we plan in this last EGX300 release to add support for Masterpact/Compact in the IFE/IFM.  We also plan to add Smartlink IP support.  I have not discussed adding the I/O module with them, and I am not sure what this effort will be...so I will check.

I am awaiting a final estimate from the validation/verification team for the release date, but I am anticipating a June release.

Will this support give what is highly desired?  What if we do not support the I/O Module?

James

FYI::

Reply
MagnusEngstrom
Ensign MagnusEngstrom Ensign
Ensign

Posted: ‎2015-04-21 11:25 PM

0 Likes
0
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-21 11:25 PM

Very good news - thanks James!

Before we had the chassis management (indication of connected - test - disconnected position) with the CCM module. This will be replaced by the IO module.

I understand that the almost infinite number of possibilities available with the free programming of the IO module will be hard to take into account, but at least the standard application no 1, chassis management, is needed.

// Magnus

Reply
AndersDahlskog
Lieutenant AndersDahlskog Lieutenant
Lieutenant

Posted: ‎2015-04-22 03:41 AM

0 Likes
0
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-22 03:41 AM

I agree with Magnus comments, the I/O module + IFM module replace the CCM module so for the cradle management and the possibility to wiew this with Micrologic in EGX300 webpage without the customer must "downgrade" the firmware in IFM is important.

Hope this can be inplemented in this upcoming firmware.

Anders

Reply
QuentinLt
Ensign QuentinLt Ensign
Ensign

Posted: ‎2015-04-23 03:10 AM

0 Likes
0
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-04-23 03:10 AM

Thanks James for working on integrating Act9 Smartlink Ethernet in EGX300 ! I'm sure plenty of countries will appreciate that !

Quentin Leddet
Offer Management, Australia
Reply
sesa77557
sesa77557 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-07-15 11:09 AM

0 Likes
3
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-15 11:09 AM

Ciao ,

do you have any update regarding the release of the new EGX300 firmware?

We are having a big issue with one Customer for the application Masterpact/Compact NS + IFM  + IO module

When do you think that we will be able to have a firmware that fix all these ?

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-07-15 01:45 PM

3 Likes
2
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-15 01:45 PM

Hi Roberto.

Yes..the team has done a great job, and is working diligently on the final stages of testing, and I am expecting the release by the end of the month.

James

Reply
sesa77557
sesa77557 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-07-16 02:05 AM

0 Likes
1
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-16 02:05 AM

Tnx James for your help!

A last question: do you confirm me that also the configuration Masterpact/Compact NS (Micrologic E) + IFM (not IFE) + IO module will be supported with all the features that today are supported in Micrologic E+CCM (included the reset of min/max values)?

Can I tell to the Customer that before the 31st of July we will be able to provide him the updated firmware?

Roberto

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-07-16 09:03 AM

0 Likes
0
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-16 09:03 AM

No problem.

Please check email for more context, but yes...this is what we plan to release.  There is still testing to be completed, but we're feeling very good about the release.

Lastly..for the release date.  We are aiming for end of July.  The only thing that I'm aware of that could post-pone this is waiting for the translations to come back, so the testers can also test with languages...OR...if something was found during our testing that requires any development change.

Thanks,

James

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of