Com'X 510 Internal IO module Interface using Modbus

Gateways and Energy Servers

Get expert answers to your questions regarding Schneider Electric Gateways & Energy Servers, from product selection to implementation and troubleshooting. Collaborate with a global community of experts and peers, get support and share your experiences by subscribing to the Schneider Electric Community Gateways and Energy Servers forum today.

mykel
Lieutenant JG
Lieutenant JG
0 Likes
9
466

Com'X 510 Internal IO module Interface using Modbus

Hi All,

 

Need your advise on how to read data connected to Com'X local AI/DI port using modbus TCP and to be Interfaced to EBO.

I read the user manual and it says that in order to access the internal AI/DI i need to use slave ID 255, but when trying it with EBO it is not possible to input 255.

 

Please refer to link User manual page 49.

 

https://www1.lk.dk/flipbooks/ComX%20510_User_Manual/content/ComX%20510%20User%20Manual.pdf 

 

Thank you.

Tags (1)
9 Replies 9
Bojan
Captain Captain
Captain
0 Likes
1
464

Re: Com'X 510 Internal IO module Interface using Modbus

Hi, do you plan PME2020 integration with EBO. as it can read slave ID 255?

Tags (1)
mykel
Lieutenant JG
Lieutenant JG
0 Likes
0
460

HiRe: Com'X 510 Internal IO module Interface using Modbus

Hi Bojan,

 

we will only use the existing Com'X as a gateway to read 2 analog points and will not use PME.

Tags (1)
Romain_Polette
Sisko Sisko
Sisko
0 Likes
3
458

Re: Com'X 510 Internal IO module Interface using Modbus

Hello @mykel , 

This question seems for an EBO Expert.

 

@Benji is there a way to connect a Com'X510 to an Enterprise Server and read the Com'X Internal Registers through Slave ID 255 ?

 

Thanks.

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France
Tags (1)
Benji
Administrator Administrator
Administrator

Re: Com'X 510 Internal IO module Interface using Modbus

Sure, you should be able to. Just add a TCP server device.

Tags (1)
mykel
Lieutenant JG
Lieutenant JG
0 Likes
0
448

Hi BRe: Com'X 510 Internal IO module Interface using Modbus

Hi Benji,

 

As i mentioned in my description, we did test it and there seems to be a warning when inputting 255 as Device ID and will not let us save it. Doing trial and error we found out that 248 will let us save the changes but will revert to INVALID after.

Please see screenshots below.

 

Modbus_SlaveID_248.jpegModbus_SlaveID_255.jpeg

 

 

Tags (1)
mykel
Lieutenant JG
Lieutenant JG
0 Likes
2
447

Re: Com'X 510 Internal IO module Interface using Modbus

Hi Romain,

 

If EBO has a restriction with 255 ID, is it possible to change the Local Device ID of Com'X instead?

Trying to look for it in the settings but failed to locate.

Kindly advice.

 

Thank you.

Tags (1)
Randi_Dolan
Commander Commander
Commander

Re: Com'X 510 Internal IO module Interface using Modbus

Hi,

 

The device ID of the Com'X is fixed at 255.  This is because it's a gateway and the Modbus standard states that it's ID is 255.

 

Randi

Tags (1)
mykel
Lieutenant JG
Lieutenant JG
0 Likes
0
435

Re: Com'X 510 Internal IO module Interface using Modbus

Hi @Benji,

 

If the slave ID is fix on 255 for Com'X, do we have a way to allow EBO to read this data?

Kindly advice.

Tags (1)
mykel
Lieutenant JG
Lieutenant JG
0 Likes
0
429

Re: Com'X 510 Internal IO module Interface using Modbus

Hi @Randi_Dolan ,

 

Thank you for confirming.

Tags (1)