COM'X510 with BCPM

Gateways and Energy Servers

Get expert answers to your questions regarding Schneider Electric Gateways & Energy Servers, from product selection to implementation and troubleshooting. Collaborate with a global community of experts and peers, get support and share your experiences by subscribing to the Schneider Electric Community Gateways and Energy Servers forum today.

Solved
sesa194528
Schneider Alumni (Retired)
Schneider Alumni (Retired)

COM'X510 with BCPM

Hello

Does the Com'x 510 support BCPM (multy circuit metering of VERIS ) by default support device?

If not, is it going to be devloped soon?

Moshe 


Accepted Solutions
sesa125183_brid
Ensign Ensign
Ensign

Re: COM'X510 with BCPM

Hi Moshe,

The BCPM is supported by the Com'X510 (FW Version 1.1.44). The Recommended number of BCPM to be connected to Com'X510 is Two BCPMs per Com'X. Hope that helps.

Best Regards,

Michael Khela

See Answer In Context

4 Replies 4
sesa125183_brid
Ensign Ensign
Ensign

Re: COM'X510 with BCPM

Hi Moshe,

The BCPM is supported by the Com'X510 (FW Version 1.1.44). The Recommended number of BCPM to be connected to Com'X510 is Two BCPMs per Com'X. Hope that helps.

Best Regards,

Michael Khela

sesa57006_bridg
Crewman Crewman
Crewman
0 Likes
1
49

Re: COM'X510 with BCPM

Michael, what is the reason for the limited recommendation of 2 BCPM's per Com'X?

sesa125183_brid
Ensign Ensign
Ensign
0 Likes
0
49

Re: COM'X510 with BCPM

Hi Jonathan,

This Recommendation is because the BCPM could support up to 84 channels which is a large number of topics that customer may be logging, so this recommendation is in-place for better performance. In addition, the EGX300 had the same recommendation for BCPM devices

Best Regards

sesa194528
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
49

Re: COM'X510 with BCPM

Thank you very much

It is very helpfull

Moshe